[RE-wrenches] UL3741 inverter listing for residential roofs

2024-07-29 Thread jay via RE-wrenches
HI All,

I”m wondering if there are any rack companies that have a listed product for 
residential roofs?

The only inverters I’ve found have been for larger commercial size.  

Living in an area with lots of flat roofs, ( OK super low slope) it would be an 
option vs micro or other power electronics

thanks in advance

jay
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] UL3741 inverter listing for residential roofs

2024-07-29 Thread Blake Gleason via RE-wrenches
Hi Jay,

Ironridge XR is 3741 listed, but only with Tesla MCIs (for now), I believe.
https://www.ironridge.com/2024/02/27/flush-mount-systems-listed-to-ul-3741/

Best,
Blake

On Mon, Jul 29, 2024 at 9:58 AM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> HI All,
>
> I”m wondering if there are any rack companies that have a listed product
> for residential roofs?
>
> The only inverters I’ve found have been for larger commercial size.
>
> Living in an area with lots of flat roofs, ( OK super low slope) it would
> be an option vs micro or other power electronics
>
> thanks in advance
>
> jay
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Blake Gleason, PE | Employee Owner
Director of Innovation and Technical Excellence
O: 510-845-2997 x128
C: 510-867-5878



1035 Folger Ave.
Berkeley, CA 94710
www.sunlightandpower.com
License #326203

  

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread William Miller via RE-wrenches
Friends:



I have been through the manual and I can’t find anywhere where you can see
on the inverter front panel the PV volts or amps for each of the MPPT
inputs.  Am I missing something?



Thanks,



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Neutral run to critical loads sub-panel

2024-07-29 Thread William Miller via RE-wrenches
Friends:



I found a grid-tie battery-backup system with a 120/240 VAC critical loads
sub-panel that has no neutral run to it.  All of the 120 VAC loads have
their neutrals land in the meter panel.



I have always felt instinctively that the neutrals should land in the
breaker panel that feeds the circuit.  I have looked through the NEC to
find a passage that spells this out but I can seem to find one.



Is this a code requirement?  Is this recommended practice?



Thanks in advance.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread MD Electric & Solar via RE-wrenches
On the touchscreen, touch the battery icon, you will find it there.

On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Friends:
>
>
>
> I have been through the manual and I can’t find anywhere where you can see
> on the inverter front panel the PV volts or amps for each of the MPPT
> inputs.  Am I missing something?
>
>
>
> Thanks,
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
Michael D Nelson
MD Electric & Solar Inc.
Office: 707-412-3181
Cell: 707-684-0064
www.mdelectricsolar.com
www.facebook.com/mdelectricandsolar
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread William Miller via RE-wrenches
MD Electric:



I touched the screen and it did not respond.  Could the display be
defective?



This unit is a 12K-P.  The serial number is blank.  I am not sure I am
looking at a manual for the 12K-P.  The Sol-Arc website shows only the
12k-2P.  Are there differences in the operation of the P versus the 2P?



Thank you for your time.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* MD Electric & Solar [mailto:mdelectricso...@gmail.com]
*Sent:* Monday, July 29, 2024 9:14 PM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Sol Ark 12 k PV monitoring



On the touchscreen, touch the battery icon, you will find it there.



On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

Friends:



I have been through the manual and I can’t find anywhere where you can see
on the inverter front panel the PV volts or amps for each of the MPPT
inputs.  Am I missing something?



Thanks,



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 

Michael D Nelson

MD Electric & Solar Inc.

Office: 707-412-3181

Cell: 707-684-0064

www.mdelectricsolar.com

www.facebook.com/mdelectricandsolar
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread MDElectricSolar via RE-wrenches
Does this unit have a touchscreen? Can you touch the settings wheel and get into the settings that way?Michael D NelsonMD Electric & Solar, Inc.707-684-0064 mobile707-884-1862 officewww.mdelectricsolar.comwww.facebook.com/mdelectricandsolarOn Jul 29, 2024, at 9:58 PM, William Miller via RE-wrenches  wrote:MD Electric: I touched the screen and it did not respond.  Could the display be defective? This unit is a 12K-P.  The serial number is blank.  I am not sure I am looking at a manual for the 12K-P.  The Sol-Arc website shows only the 12k-2P.  Are there differences in the operation of the P versus the 2P? Thank you for your time. William Miller Miller Solar17395 Oak Road, Atascadero, CA 93422805-438-5600www.millersolar.comCA Lic. 773985  From: MD Electric & Solar [mailto:mdelectricso...@gmail.com] Sent: Monday, July 29, 2024 9:14 PMTo: will...@millersolar.com; RE-wrenchesSubject: Re: [RE-wrenches] Sol Ark 12 k PV monitoring On the touchscreen, touch the battery icon, you will find it there. On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches  wrote:Friends: I have been through the manual and I can’t find anywhere where you can see on the inverter front panel the PV volts or amps for each of the MPPT inputs.  Am I missing something? Thanks, William Miller Miller Solar17395 Oak Road, Atascadero, CA 93422805-438-5600www.millersolar.comCA Lic. 773985  ___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org -- Michael D NelsonMD Electric & Solar Inc.Office: 707-412-3181Cell: 707-684-0064www.mdelectricsolar.comwww.facebook.com/mdelectricandsolar  
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol Ark 12 k PV monitoring

2024-07-29 Thread William Miller via RE-wrenches
Michael:



This is my first experience with a Sol-Arc and I did not install it.  I
touched the screen gently and then less gently. There was no response.  I
could only navigate by using the arrow keys.



I see now there is a frozen touch screen recovery procedure.  It involves
pressing the Esc button for 7-10 seconds.  I will try that.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* MDElectricSolar [mailto:mdelectricso...@gmail.com]
*Sent:* Monday, July 29, 2024 10:21 PM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Sol Ark 12 k PV monitoring



Does this unit have a touchscreen? Can you touch the settings wheel and get
into the settings that way?

Michael D Nelson

MD Electric & Solar, Inc.

707-684-0064 mobile

707-884-1862 office

www.mdelectricsolar.com

www.facebook.com/mdelectricandsolar





On Jul 29, 2024, at 9:58 PM, William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:



MD Electric:



I touched the screen and it did not respond.  Could the display be
defective?



This unit is a 12K-P.  The serial number is blank.  I am not sure I am
looking at a manual for the 12K-P.  The Sol-Arc website shows only the
12k-2P.  Are there differences in the operation of the P versus the 2P?



Thank you for your time.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* MD Electric & Solar [mailto:mdelectricso...@gmail.com]
*Sent:* Monday, July 29, 2024 9:14 PM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Sol Ark 12 k PV monitoring



On the touchscreen, touch the battery icon, you will find it there.



On Mon, Jul 29, 2024 at 8:52 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

Friends:



I have been through the manual and I can’t find anywhere where you can see
on the inverter front panel the PV volts or amps for each of the MPPT
inputs.  Am I missing something?



Thanks,



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 

Michael D Nelson

MD Electric & Solar Inc.

Office: 707-412-3181

Cell: 707-684-0064

www.mdelectricsolar.com

www.facebook.com/mdelectricandsolar





___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org