[RE-wrenches] Radian Question

2023-10-29 Thread Drake Chamberlin via RE-wrenches

My Radian GS 8048 intermittently will connect to the grid to charge
batteries. The grid voltage seems to run high around here. Yesterday, it
wouldn't connect. The grid voltage was at 251 V. Later it did connect.
At that point the grid was at 246 V. 


I am suspecting that the Radian has a voltage acceptance limit of 250 V.
Is that true? Is it possible to open up the window? 

If that isn't it, what could be the problem? 

Thank you, 

Drake 

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_ 


--___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Radian Question

2023-10-29 Thread Jay via RE-wrenches
Hi drake

The early mate 3 has a glitch which I think they changed in the 3s. 

You e got to set the rebulk volts above what you want it to charge at. 

IE if the battery volts don’t get below the rebulk volts it won’t charge. 

So if your shallow cycling the batteries it’s common it won’t get below the 
rebulk volts. If you’re deep cycling it usually will with default settings 

The default high voltage window for ac input is default at 140v. 

Hope this helps

Jay





> On Oct 29, 2023, at 11:14 AM, Drake Chamberlin via RE-wrenches 
>  wrote:
> 
> 
> My Radian GS 8048 intermittently will connect to the grid to charge 
> batteries. The grid voltage seems to run high around here. Yesterday, it 
> wouldn't connect. The grid voltage was at 251 V. Later it did connect. At 
> that point the grid was at 246 V.
>  
> I am suspecting that the Radian has a voltage acceptance limit of 250 V. Is 
> that true? Is it possible to open up the window?
>  
> If that isn't it, what could be the problem?
>  
> Thank you,
>  
> Drake
>  
> Drake Chamberlin
> 
> Athens Electric LLC
> 
> Ohio Electrical Contractor’s License 44810
> 
> NABCEP Certified PV Installation Professional
> 
>  
> 
> 
> --
>  
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling

2023-10-29 Thread Kienan Maxfield via RE-wrenches
William,

My whole email is in regards to the point you made when you said
"This is not how battery inverters were originally designed to operate.  These 
systems require careful consideration to avoid battery overcharging."

I both agree and disagree with these statements... depending on what you mean. 
I don't think it's super helpful to say that careful considerations are 
required without mentioning what those considerations are, and I'll get to 
those below.





When you say that the battery inverters "weren't originally designed for this" 
I'd agree to an extent.. The "original" battery based inverters 25 years ago 
were certainly not designed for AC coupling. They weren't "originally" designed 
for it. But that was then and this is now.





Now William is correct that the Gen input becomes an AC output, and you can't 
wire the gen into that "input" if you are using it as a PV input... that being 
said, Jay didn't think otherwise, he was just critiquing the wiring diagram in 
the original post to say that it wires up differently, so I'd say that you are 
both right on this one. That said, I don't think anyone says you have to wire 
it into the gen port, I think that even with the hybrid inverters, the way in 
William's original post is still a fully acceptable way to do it.



I am not a huge fan of AC coupling, however, I have done it a fair amount and I 
have a fair amount of experience with it off-grid with Lithium and with Lead 
Acid. Most of my experience is with Outback and Victron, but I have some 
experience with Schneider as well. These systems have been working really well 
for a good while, but that being said, Schneider had some real problems at 
first (major headache).


Now when it comes to hybrid inverters, I'm still not a huge fan... but I'm 
starting to try them out. I have not tested AC coupling with any of them yet. I 
was at a conference less than a year ago and one of the major brands was saying 
that there is no hybrid inverter that supports both AC coupled PV and a 
generator at the same time for a grid tied system. They said "you can't have it 
all." There may be an exception to that, I've never looked into it, but with 
the Victron and Outback (and probably Scheider... IDK) it's easy to have it 
all. I've done it and it works well in every mode. The frequency changes super 
fast and assuming you have a properly programmed rule 21 compliant Grid tied 
inverter, it responds very quickly, and in the systems I've monitored, the 
frequency never had to go above 62 Hz, which is good enough for most sensitive 
loads. The inverters are totally designed for this these days, but if you have 
highly sensitive loads, then it may not work well.



Considerations...
First of all, I will be assuming that you are using quality rule 21 grid-direct 
inverters and a good battery inverter that works as well as the Outback Radian 
or the Victron. The early Schneiders were too slow in changing their frequency, 
and special considerations had to be accounted for because of that, but I heard 
that was fixed a while ago. You had to reduce the charging voltages to account 
for the delayed throttling, but I can attest that even in the early days, 
Outback never had this problem, and Victron works smoothly as well.

The primary problem for AC coupling is in off-grid scenarios or prolonged power 
outages, and that's the black start issue (or dark start). Simply put, if your 
battery gets low and the battery inverter turns off, then your PV can't charge 
the battery. This problem is lessened when you connect the PV Grid Direct 
inverters to a dedicated output on the inverter so that the loads shut down 
while the battery is still a few percent above the inverter shutdown level. 
That is a nice advantage of the Victron inverters. I don't know if the Hybrid 
inverters do this or not. In any case, even with this little safety net, the 
inverter can still discharge the battery to the point where the inverter turns 
off and you have a problem. My solution is that you should have at least a 
little bit of the PV DC coupled so that when the sun comes out, the voltage 
will rise and the inverter will turn on. This is also recommended in Victron's 
AC Coupling manual.

The second consideration is the minimum inverter size... Your battery based 
inverter needs to be capable of handling and controlling the full PV power. 
Victron recommends that the maximum PV power (DC or AC, whichever is lower) 
does not exceed 100% of the rating of the inverter (no more than 10kW of power 
from the PV on a 10kW inverter). Outback recommends no more than 6 kW of 
Grid-Tied inverter per 8 kW of Radian (so that's 75% of the battery inverter's 
power). In some circumstances, this could demand upsizing the battery inverter, 
which is another great reason to DC couple half of the PV and AC couple the 
other half... because then you could effectively have more PV with less battery 
based inverter, depending on your loads.

As was ment