[RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Drake

Hello Wrenches,

I am going to AC couple some Enphase inverters and found some really 
nice solid state, single pole relays to control them with. Enphase 
says I must use 2 pole relays for the control current even though the 
disconnects will turn off all power for maintenance.


Enphase claims that the inverters will not shut down reliably with 
only one line opened. This does not make sense to me in view of UL 
1741. Is Enphase correct in their claim, or are there other reasons 
that both poles need to be opened


I want to use the solid state relays because the coil voltage is 
between 3 and 32 volts. This would avoid the need to add voltage 
dropping series resistors to protect the coil for higher battery voltages.


Alternatively, does anyone know of reasonably priced, 2 pole solid 
state relays?


Thanks,

Drake


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread James Jefferson Jarvis

On 8/28/2017 8:44 AM, Drake wrote:

Alternatively, does anyone know of reasonably priced, 2 pole solid state
relays?


Just use two single pole SSRs. One for each leg. There are two pole SSR, 
but the price is not going to be bargain basement.


-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
www.aprsworld.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Nick Soleil
You can use a one-pole relay.  We show one-pole switching in our zero-export, 
self-consumption doc for PEL applications.

Nick Soleil
Field Application Engineer
Enphase Energy
Cell: 707-321-2937

On Aug 28, 2017, at 6:44 AM, Drake 
mailto:drake.chamber...@redwoodalliance.org>>
 wrote:

Hello Wrenches,

I am going to AC couple some Enphase inverters and found some really nice solid 
state, single pole relays to control them with. Enphase says I must use 2 pole 
relays for the control current even though the disconnects will turn off all 
power for maintenance.

Enphase claims that the inverters will not shut down reliably with only one 
line opened. This does not make sense to me in view of UL 1741. Is Enphase 
correct in their claim, or are there other reasons that both poles need to be 
opened

I want to use the solid state relays because the coil voltage is between 3 and 
32 volts. This would avoid the need to add voltage dropping series resistors to 
protect the coil for higher battery voltages.

Alternatively, does anyone know of reasonably priced, 2 pole solid state relays?

Thanks,

Drake


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Drake

Hi Nick,

That is very good news. I just hit the wall trying to find 2 pole 
solid state N/C relays.  I was trying to decide whether to go back to 
mechanical or buy double the amount of single pole relays.


Thanks,

Drake

At 11:20 AM 8/28/2017, you wrote:

Content-Language: en-US
Content-Type: multipart/alternative;
boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"

You can use a one-pole relay.  We show one-pole switching in our 
zero-export, self-consumption doc for PEL applications.


Nick Soleil
Field Application Engineer
Enphase Energy
Cell: 707-321-2937

On Aug 28, 2017, at 6:44 AM, Drake 
<drake.chamber...@redwoodalliance.org> 
wrote:



Hello Wrenches,

I am going to AC couple some Enphase inverters and found some 
really nice solid state, single pole relays to control them with. 
Enphase says I must use 2 pole relays for the control current even 
though the disconnects will turn off all power for maintenance.


Enphase claims that the inverters will not shut down reliably with 
only one line opened. This does not make sense to me in view of UL 
1741. Is Enphase correct in their claim, or are there other reasons 
that both poles need to be opened


I want to use the solid state relays because the coil voltage is 
between 3 and 32 volts. This would avoid the need to add voltage 
dropping series resistors to protect the coil for higher battery voltages.


Alternatively, does anyone know of reasonably priced, 2 pole solid 
state relays?


Thanks,

Drake


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] PG&E Net metering Vs Smart Meters

2017-08-28 Thread William Miller
Dear Wrenches:



Here in PG&E territory we have a unique situation:  In the early days of
net metering the PG&E accounts were handled regionally.  In the early
2000s, this was all transferred to corporate in San Francisco.  In the
process PG&E lost many files.  Over the years I have had eight or so
customers come to me to seek assistance renegotiating a contract that did
exist but PG&E has no record of.



This usually happens as a result of installation of a SMART meter.  The old
mechanical meters gave customers credit whether or not the account was in
place for interconnection.  The SMART meters will not give credit unless
the account is programmed to do so.



It was my understanding that a PG&E smart meter, without being associated
with a Net Metering account, would charge a customer for the energy
exported to the grid.  PG&E is telling me that is not true.  This makes a
difference when calculating credits for these customers when signing them
back up to net meter.



Does anyone have any information on how the PG&E smart meters handle this
scenario.



By the way, I have developed a modest expertise and some contacts to help
me deal with utilities in these situations.  I can offer to assist if
anyone wants.  Contact me off-line.



Thanks in advance,



William



[image: Gradient Cap_mini]
Lic 773985
millersolar.com 
805-438-5600
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Fluke 337 DC Clamp meter vs Outback

2017-08-28 Thread Foxfire Energy
My fluke 337 DC clamp meter is consistently reading about 10 A less than what 
I'm seeing on the flex max and Mate3.. Outback tells me my fluke is lame.. Bad 
sushi?

Dan Brown 
Foxfire Energy Corp.
(802)-483-2564
www.Foxfire-Energy.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fluke 337 DC Clamp meter vs Outback

2017-08-28 Thread Dave Angelini Offgrid Solar
Looks like you need a 2nd meter to test the sushi...  --Dave


Dave Foxfire EnergyDave
> My fluke 337 DC clamp meter is consistently reading about 10 A less than
> what I'm seeing on the flex max and Mate3.. Outback tells me my fluke is
> lame.. Bad sushi?
>
> Dan Brown
> Foxfire Energy Corp.
> (802)-483-2564
> www.Foxfire-Energy.com
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Schletter S3 Rails engineering specs or tech data sheet?

2017-08-28 Thread Howard Arey
Hello Wrenches.

 

We have a BI who wants to see the spec sheet for the S3 rails we have used
on one of our solar pergola structures.

 

Trying to contact Schletter to obtain but.does anybody have a tech data
sheet or tech reference for this rail.

 

Howard "Scot" Arey

254-300-1228

scot.a...@solarcentex.com  

 



 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fluke 337 DC Clamp meter vs Outback

2017-08-28 Thread Jay
Hi Dan

You can use the shunt MV reading via say fluke 87 to double check the amps that 
your clamp on is reading. 

Jay

> On Aug 28, 2017, at 2:47 PM, Dave Angelini Offgrid Solar 
>  wrote:
> 
> Looks like you need a 2nd meter to test the sushi...  --Dave
> 
> 
> Dave Foxfire EnergyDave
>> My fluke 337 DC clamp meter is consistently reading about 10 A less than
>> what I'm seeing on the flex max and Mate3.. Outback tells me my fluke is
>> lame.. Bad sushi?
>> 
>> Dan Brown
>> Foxfire Energy Corp.
>> (802)-483-2564
>> www.Foxfire-Energy.com
>> ___
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fluke 337 DC Clamp meter vs Outback

2017-08-28 Thread Dana
When or have you ever had it recalibrated esp. if it has a few miles on it?
I was getting floating readings  & I sent my 25 year old fluke in a few years 
ago & definitely saw more accurate readings and the floaties went away.


Dana Orzel   Great Solar Works, Inc. 
208.721.7003   d...@solarwork.com
Idaho Contractor - # 028765  Idaho PV # 028374
NABCEP # 051112-136   www.solarwork.biz
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.


-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Foxfire Energy
Sent: Monday, August 28, 2017 2:48 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Fluke 337 DC Clamp meter vs Outback

My fluke 337 DC clamp meter is consistently reading about 10 A less than what 
I'm seeing on the flex max and Mate3.. Outback tells me my fluke is lame.. Bad 
sushi?

Dan Brown 
Foxfire Energy Corp.
(802)-483-2564
www.Foxfire-Energy.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Drake

Hi Nick,

I should mention that the inverters being AC coupled are M-250s, not 
the new IQ series. Would that make any difference?


Thanks,


Drake


At 03:12 PM 8/28/2017, Drake wrote:

Hi Nick,


At 11:20 AM 8/28/2017, you wrote:

Content-Language: en-US
Content-Type: multipart/alternative;
boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"

You can use a one-pole relay.  We show one-pole switching in our 
zero-export, self-consumption doc for PEL applications.


Nick Soleil
Field Application Engineer
Enphase Energy
Cell: 707-321-2937

On Aug 28, 2017, at 6:44 AM, Drake 
< 
drake.chamber...@redwoodalliance.org> wrote:



Hello Wrenches,

I am going to AC couple some Enphase inverters and found some 
really nice solid state, single pole relays to control them with. 
Enphase says I must use 2 pole relays for the control current even 
though the disconnects will turn off all power for maintenance.


Enphase claims that the inverters will not shut down reliably with 
only one line opened. This does not make sense to me in view of UL 
1741. Is Enphase correct in their claim, or are there other 
reasons that both poles need to be opened


I want to use the solid state relays because the coil voltage is 
between 3 and 32 volts. This would avoid the need to add voltage 
dropping series resistors to protect the coil for higher battery voltages.


Alternatively, does anyone know of reasonably priced, 2 pole solid 
state relays?


Thanks,

Drake


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org


Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 



List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 



List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fluke 337 DC Clamp meter vs Outback

2017-08-28 Thread Drake
Some years ago I was talking to Outback Tech support and mentioned 
major discrepancies in voltage readings from a Mate. The support lady 
laughed and said that the meters on the Outback weren't accurate.


At 04:48 PM 8/28/2017, you wrote:
My fluke 337 DC clamp meter is consistently reading about 10 A less 
than what I'm seeing on the flex max and Mate3.. Outback tells me my 
fluke is lame.. Bad sushi?


Dan Brown
Foxfire Energy Corp.
(802)-483-2564
www.Foxfire-Energy.com
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupled Enphase

2017-08-28 Thread Nick Soleil
The one-pole relay will work for de-energizing any of the Enphase 
microinverters.

Nick Soleil
Field Application Engineer
Enphase Energy
Cell: 707-321-2937

On Aug 28, 2017, at 6:03 PM, Drake 
mailto:drake.chamber...@redwoodalliance.org>>
 wrote:

Hi Nick,

I should mention that the inverters being AC coupled are M-250s, not the new IQ 
series. Would that make any difference?

Thanks,


Drake


At 03:12 PM 8/28/2017, Drake wrote:
Hi Nick,


At 11:20 AM 8/28/2017, you wrote:
Content-Language: en-US
Content-Type: multipart/alternative;
 boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"

You can use a one-pole relay.  We show one-pole switching in our zero-export, 
self-consumption doc for PEL applications.

Nick Soleil
Field Application Engineer
Enphase Energy
Cell: 707-321-2937

On Aug 28, 2017, at 6:44 AM, Drake < 
drake.chamber...@redwoodalliance.org>
 wrote:

Hello Wrenches,

I am going to AC couple some Enphase inverters and found some really nice solid 
state, single pole relays to control them with. Enphase says I must use 2 pole 
relays for the control current even though the disconnects will turn off all 
power for maintenance.

Enphase claims that the inverters will not shut down reliably with only one 
line opened. This does not make sense to me in view of UL 1741. Is Enphase 
correct in their claim, or are there other reasons that both poles need to be 
opened

I want to use the solid state relays because the coil voltage is between 3 and 
32 volts. This would avoid the need to add voltage dropping series resistors to 
protect the coil for higher battery voltages.

Alternatively, does anyone know of reasonably priced, 2 pole solid state relays?

Thanks,

Drake


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328

___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] SolarEdge tech help

2017-08-28 Thread Jeremy Rodriguez
Does anyone have a dealer only phone number to reach SolarEdge tech support?


Jeremy Rodriguez 
Solar Installation And 
Design Expert 
All Solar, Inc.
1463 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand!
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org