In Offgrid mode the inverter is not in a software function of selling like it 
is in self consumption. It syncs to the grid and follows the grid not the other 
way around thus the hardware is incapable of selling. Selling requires the 
inverter to try and push the voltage higher than the grid to create energy flow.

So there is no hardware prevention its strictly software, Just the same as the 
Outback, Magnum, Schneider etc. When in off grid mode it follows the grid vs in 
sell mode it drives the grid.


Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:[email protected]]

From: Lou Russo <[email protected]>
Sent: Thursday, June 26, 2025 8:44 AM
To: RE-wrenches <[email protected]>
Cc: Jason Szumlanski <[email protected]>; Sue Stankevitz 
<[email protected]>
Subject: Re: [RE-wrenches] Truly Zero Export

Aloha All,

Thank you Sue for the detailed explanation of the self-consumption and off-grid 
operating modes of the AIO.
We have a follow-up question regarding the off-grid mode operation that we'd 
like to clarify :
In off-grid mode, what specific mechanical or electrical mechanisms absolutely 
prevent any export to the grid side? Yet (if I understand your email 
correctly), still allows for grid passthrough.

This information will help us when speaking with AHJs and utility engineers who 
need to understand the export prevention safeguards for permitting and 
interconnection approval, plus I am just super interested in how it works!
Thank you!

Aloha,
Lou Russo
Spree Solar Systems LLC
C-34322





On Thu, Jun 26, 2025 at 1:47 AM Sue Stankevitz via RE-wrenches 
<[email protected]<mailto:[email protected]>> 
wrote:
In a self-consumption style situation an inverter sells to drop the usage to 
close to 0 watts. It’s a controlled sell as not to export. The inverter “buys” 
power from the grid at a low rate to power the first 200w or so of the load. 
This is designed to prevent accidental selling during large load fluctuations 
but is not an absolute guarantee against very small very short duration sells.

In Off Grid mode it does not sell it just makes power on the AC Out side. 
Similar to what you may be familiar with in the old Outback or Magnum 
inverters. If the AC in is present it passes through and runs the loads if its 
not present the inverter powers the loads.

To complement this for a self use style system you run the grid into the 
Generator in not AC in and program the generator to start and stop at your 
desired levels and then the AIO will ignore the grid when the battery is above 
your programmed set points similar to the Rosie in VDC disconnect/connect

Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:[email protected]]

From: Jason Szumlanski 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, June 25, 2025 12:12 PM
To: Sue Stankevitz <[email protected]<mailto:[email protected]>>
Cc: RE-wrenches 
<[email protected]<mailto:[email protected]>>
Subject: Re: [RE-wrenches] Truly Zero Export

Thanks, Sue. Your response is greatly appreciated.

Can I ask how the Midnite AIO accomplishes this in Off-Grid mode? Does the 
inverter turn off grid-passthrough to the loads altogether and just offer grid 
voltage to the charger while inverting power from the batteries and solar to 
cover the loads? How does the inverter definitively "catch" excess solar 
production when a large load is dropped?

I believe what you are saying is true, but I am interested in the mechanics 
behind this. I would like to share it with our local electric co-op's chief 
engineer. They are raising red flags with the local AHJ for homes that install 
solar panels that don't net meter, even if there is no intention of net 
metering.


Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Wed, Jun 25, 2025 at 11:48 AM Sue Stankevitz 
<[email protected]<mailto:[email protected]>> wrote:
For the MidNite MN15-12K-AIO it has 2 modes that pertain to this discussion

Off Grid mode will never export out the input terminals at all no matter what
Self Consumption will export out the input terminals to the Main Panel to try 
and zero the CT’s out. We have a setting you can adjust that will always draw 
this amount first from the grid to give the inverter some room to catch the 
over shoots when loads turn off. We find around 200 Watts is generally a good 
spot.

For the MidNite MNROSIE7048RE it has 2 modes as well
Grid Support- This allows Rosie to try and zero the incoming power from the 
grid any time the battery is above a set point you select. Rosie will always 
draw the first 150-200 watts from the grid to allow it to catch the over shoots 
when a load goes away
VDC Connect / Disconnect- This mode allows Rosie to open its relay any time the 
battery is above a value you select eliminating ANY possibility of over shoot 
when loads go away.

If you are working with a municipality where there is absolutely zero room for 
error it is best practice to use the more conservative approach of Off Grid 
Mode or VDC Connect/Disconnect to insure there will never be a chance of export 
however slim or minior.
Sue Stankevitz
MidNite Solar, Inc.<https://www.midnitesolar.com/index.php>
(360) 403-7207 (XT122)
[cid:[email protected]]

From: RE-wrenches 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Jason Szumlanski via RE-wrenches
Sent: Wednesday, June 25, 2025 2:59 AM
To: RE-wrenches 
<[email protected]<mailto:[email protected]>>
Cc: Jason Szumlanski 
<[email protected]<mailto:[email protected]>>
Subject: [RE-wrenches] Truly Zero Export

We've had issues with Enphase systems "leaking" electricity back to the utility 
grid despite being in a no export grid profile. A local utility company gets 
all bent out of shape if there is even a watt-hour of reverse meter feed in 
detected. I understand why it isn't feasible to completely prevent this with 
Enphase's system architecture, even with a sizeable battery.

Off-grid inverters that can't interact with the grid will obviously provide no 
export.

My question is about hybrid inverters that are capable of grid sell, but 
programmed not to sell. Are they capable of truly Zero Export?

The AIOs with grid pass-through don't seem likely to prevent reverse current 
flow, but I could be wrong. I'm not sure I would trust Sol-Ark to stop grid 
sell completely. Midnite AIO isn't well enough documented to understand how off 
grid mode works. The EG4 18Kpv has some cryptic settings that seem to imply it 
has truly a off grid mode, but I'm not sure how that works, either.

If not AIOs, what about other system architectures? I find it hard to believe 
that a Powerwall 3 could operate in a non-grid-interactive manner. After all, 
it doesn't even support fully off-grid operation. An EG4 FlexBoss/GridBoss 
setup would naturally rely on current transformers to prevent grid export, 
which is a deal breaker I would think in any method to prevent grid selling. 
Other AC Coupled solutions like Franklin seemingly have no chance of preventing 
export entirely.

It seems the only way for true no export to work is to invert battery power at 
all times, meaning no grid pass-through and no AC Coupling. The 
inverter/charger need to operate simply as a load from the grid perspective. 
Can any grid interactive inverter system programmatically change its mode 
entirely to prevent grid selling?


Jason Szumlanski
Florida Solar Design Group

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
[email protected]<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to