Hi William, Yes, we have run into this for the past couple of years since the 2020 NEC went into effect 1/1/2023 in CA. At first we thought it was PG&E that had the requirement, but then found out it was the NEC and I believe PG&E will enforce it as well. There was misinformation from electricians who thought that the old "California 4" type panel with two 200 A main breakers was no longer allowed by PG&E. In fact, they are still allowed, but just need to have the 2020 NEC-compliant separate disconnect partiations.
This is the Siemens brochure with more information: https://s3.amazonaws.com/dcc-data-extract/new-delta/asset/Compas/daily/Compas/Marketing%20Flyer/SIE_FL_230-71_MeterMain.pdf?100822 Best, August On Thu, Mar 27, 2025 at 4:22 PM William Miller via RE-wrenches < [email protected]> wrote: > Friends: > > > > I have ordered a Class 320 Meter/Main/Combo. My vendor informs me there > are new codes that apply to these cans, specifically in 230.71(B), cited > below: > > > > *(B) Two to Six Service Disconnecting Means. *Two to six service > > disconnects shall be permitted for each service permitted by > > 230.2 or for each set of service-entrance conductors permitted > > by 230.40, Exception No. 1, 3, 4, or 5. The two to six service > > disconnecting means shall he permitted to consist of a combination > > of any of the following: > > (1) Separate enclosures with a main service disconnecting > > means in each enclosure > > (2) Panelboards with a main service disconnecting means in > > each panelboard enclosure > > (3) Switchboard(s) where there is only one service disconnect > > in each separate vertical section where there are > > barriers separating each vertical section > > (4) Service disconnects in switchgear or metering centers > > where each disconnect is located in a separate compartment > > > > > > Here is an analysis, apparently from Siemens: > > > > > > Apparently there are factory partitions required now and some models have > them and some do not. Of course the one I specified, advocated for and > that is cheaper does not have the partition. I don’t want to order the > wrong one so I am looking for verification I am understanding this > correctly. > > > > Have any of you run up against this when ordering these devices or having > them approved? > > > > Thanks in advance for any input! > > > > William Miller > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org > >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org