Hello,

This system consists of -2- parallel Envy 12kw inverters and -2- evault
18.5kwh batteries. Grid tied w/about 13kw of pv on each inverter. Closed
loop of course.

I presently have the batteries set to charge off the grid when batteries
fall to 90% SOC, stop charging when they rise to 95%.

When I first commissioned the system, we noticed that whenever the grid
switched to/from battery start or stop charging, lighting in the building
would flicker momentarily AND the electronic t-stat for the furnace would
power down and had to be reset manually.

I found a parameter in the inverter called "seamless switch" and enabled
it. This supposedly shortens the switch over between states from 200ms to
50ms. That was enough to keep the t-stat operational, but not all the
lights from flickering.

Oddly enough, the older 4ft fluorescent ballasted lighting stopped
flickering, but the newer styles, a mix of compact fluorescent and LED,
still flicker some.

Any experience out there with something like this? Are there any other
parameters I can alter to try and remedy this? I do have a support ticket
to Fortress, and in the meantime, I'm lucky to present this issue to the
vast expertise of this forum.

PS I really wish Fortess would come up with a clearer explanation of what
these setpoints do and how they interact. And consistency of labelling
access across the apps.

Amongst other things, some are not available remotely, like the "seamless
switch". The remote app lays the settings out differently, and is not
consistent in labelling similar functions between the app and the LCD
setting page on the inverter. And as mentioned before, little to zero
detail in the app documentation.

-- 

*Kirk Herander / **kirkh@vermont.solar <kirkh@vermont.solar>*

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to