The APsmart units have a history of rapid failure due to crosstalk.  You 
absolutely MUST keep the DC conductors separate.  Don’t risk it.  They fail by 
thermal event.

Keeping the APsmart away from wires and other objects is a good idea to 
mitigate thermal event risk.  Keep wires inside the module frame and the 
APsmart under (or vice-versa, though if against the glass a thermal event will 
cause failure of module).

APsmart has lots of unusual installation instructions compared with standard 
best practices. It is probably best to speak with the manufacturer to clarify 
and ensure you have their most recent manual.

Regards,

Matt


Matt Partymiller
General Manager
Solar Energy Solutions, LLC
Lexington | Louisville | Bloomington | Cincinnati | Evansville | Indianapolis
859-312-7456 (Office)
877-312-7456 (General)
m...@sesre.com

Check out our amazing new website and social media updates: 
www.sesre.com<http://www.sesre.com/>
[cid:image006.png@01DB2B7F.B6513D60]<http://www.sesre.com/> 
[cid:image007.png@01DB2B7F.B6513D60] 
<https://www.facebook.com/SolarEnergySolutionsLLC>  
[cid:image008.png@01DB2B7F.B6513D60] 
<https://www.instagram.com/solarenergysols>  
[cid:image009.png@01DB2B7F.B6513D60] <https://twitter.com/SolarEnergySols>  
[cid:image010.png@01DB2B7F.B6513D60] <https://www.linkedin.com/company/sesre>



From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Dave 
Tedeyan via RE-wrenches
Sent: Thursday, October 31, 2024 9:57 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Cc: Dave Tedeyan <d...@sungineersolar.com>
Subject: [RE-wrenches] APS rapid shutdown

Caution: This email originated from outside SES. Do not click links or open 
attachments unless you recognize the sender and know the content is safe.

Hi All,

I am about to use the AP systems rapid shutdown units for the first time 
(pairing with SMA inverters). I was reading through the manual and came across 
a couple things that I am wondering if others have noticed issues with:

1. The manual states that you need to keep the PV conductors from each inverter 
(there are two in this system) separate, or else there may be crosstalk. So 
this would imply that you need to have two separate DC conduits from the roof 
to the inverters, rather than one. Has anyone noticed if this is truly a 
concern?

2. The manual also states that there needs to be at least 20cm (or ~8") from 
the RSD-S-PLC to another piece of equipment (other than the module it is 
mounted on). I am attaching a diagram from the manual, but it sounds like if 
you have three rows of modules, the RSD's need to be installed on the top of 
the top row, the bottom of the bottom row, and you need an 8" gap between the 
rows for the middle row. The diagram in the manual makes this more clear than 
my words can. But has anyone not installed this large gap and had issues, or 
did it still work just fine?

3. Lastly, I don't see a mention in the manual, but is there a string length 
minimum? For some reason I thought with some of the older Tigo RSD units you 
needed at least 5 or 6 in a string, or maybe I am thinking of SolarEdge 
optimizers. I just want to make sure there is no minimum, since another job 
coming up will have a string of 3 panels.

I appreciate your experience!
Cheers,
Dave

--

[Logo]<https://www.sungineersolar.com/>
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com<http://www.sungineersolar.com/>
c: (607) 270-0370

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to