Is it possible that a load shut off, and then the controllers over shot the voltage long enough to shut the BMS off?  If so, what's the solution? Lower absorb voltages?  I checked voltage calibration between the various pieces of equipment.

Ray

On 8/27/2024 4:14 PM, Jerry Shafer via RE-wrenches wrote:

High voltage disconnect would do this, is the site monitored

Fun times


On Tue, Aug 27, 2024, 2:47 PM jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    I have a buddy in tech support at Fortress.

    I asked him and he said that elevated absorb volts above 55.2
    could cause this situation.
    And then the power cycle would reboot the BMS.

    I am presuming its open loop, and the fact you mentioned that
    there was more PV and then the shut down sure might be connected.
    You might check the charge voltages/time to make sure they are
    correct and I can’t remember if the classic has battery sense wire
    connections.

    jay







    On Aug 27, 2024, at 2:51 PM, Ray Walters via RE-wrenches
    <re-wrenches@lists.re-wrenches.org> wrote:

    The SPD was on one of the PV inputs before it came into the
    house.  There were two Classics, each fed with its own PV input
    and SPD.  It actually caused an underground splice to fail (high
    resistance) which I replaced the splice and restored full
    voltage, and both Classics were working fine.  Just seems
    unlikely ( but not impossible) that the surge would make it past
    the Classic without damage, but then damage the Fortress BMS in
    an otherwise imperceptible manner.   That is our current best
    theory at the moment though.   I added an SPD on the 48 v buss,
    before this latest total shutdown.

    Ray Walters

    On 8/27/2024 2:35 PM, Dave Angelini Offgrid Solar via RE-wrenches
    wrote:
    When I have had someone lose an SPD (I assume it was on DC buss)
    there is often latent damage (shows up later) to many of the
    devices.  In a Hi Rel mode, it is recommended to replace it all.
    Most offgrid is not that critical but try telling that to
    someone with rotten food.
    The freezers and reefers are often full of spoils that smells
    never go away. YUK !
*Dave Angelini Offgrid Solar "we go where powerlines don't"
    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/
    <https://offgridsolar1.com/><http://members.sti.net/offgridsolar/>
    e-mail offgridso...@sti.net text 209 813 0060*


    On 2024-08-27 1:02 pm, Ray Walters via RE-wrenches wrote:

    Greetings All;

    I have Fortress Battery installation with a pair of E Vault
    batteries set up in a Master/ Slave arrangement.  Its been
    working fine for over a year, but the customer just had a
    complete shutdown of the batteries which left multiple
    freezers, and refrigerator with rotting food.   When he
    rebooted the batteries by turning on/off the main breaker on
    each, they both come up and showed 100% SOC on the Master, and
    98% on the other.    There were no fault codes.   I just
    recently installed a larger PV array, and so the system has
    been reaching full charge every morning.

    I have multiple calls in to Fortress, but not hearing anything
    back from them at all. We did have a lightning surge event a
    few months ago, that damaged a Midnite SPD (first ever for me),
    and took out the control board on the generator.  One VFX
    inverter has an LED out, but we only use two inverters of the
    Quad stack, so I just switched to another inverter.  All other
    equipment appeared fine: Midnite controllers, rest of the
    Outback VFX quad stack, and never any issues seen with the
    Fortress batteries.

    The other odd thing, is since he rebooted the batteries, the
    system is working fine, and recharging to 100%  by 9:30 am as
    before.    Is it possible the Fortress BMS were damaged and are
    now having an intermittent shutdown issue?  I did ask him to
    temporarily disconnect the comms between batteries, in case it
    is a bad BMS on one, it will isolate it from the other.

    This is a tough one to figure out, since it hasn't happened
    again, and there are no fault codes.  The Mate 3 shows a low
    frequency AC code, but that's usually just from the generator
    shutting down.    Any help, ideas, experiences, would be
    greatly appreciated.

    Thanks,

    Ray Walters
    Remote Solar

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't
    work, try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here:http://re-wrenches.org

    List Address:RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work, try the 
other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to