I have done it many times. YES terminate the secondary first.  As an older
CT is a step up the voltage transformer and can generate thousands of
volts.  Many of new type Cats are low voltage output and are safe to work
with.

On Fri, Mar 8, 2024, 10:46 AM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Wrenches
> Per manufacturer recommended installation procedures you must have the CT
> terminated befor the load connection can made and yes this can damage the
> CT. Depending on what you are connecting to there may also be a "short pin"
> to prevent component damage so keep that in mind when commissioning a
> logger.
> Regarding your question about hand heldsi have seen failures of cheaper
> units, l have Flukes and never had an issue with them
> Fun times
>
> On Fri, Mar 8, 2024, 8:30 AM Sam Haraldson via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Dear Wrenches,
>>
>> I'm trying to determine whether or not it is acceptable to clamp
>> monitoring CTs around hot conductors.  For this question please assume the
>> CT wires are landed in their proper terminals and that proper PPE/safety
>> protocol is employed.  The monitored currents in question are residential
>> services of 600A or less. Is there harm to the CT by clamping them around a
>> hot conductor?
>>
>> The physics of a CT from my brief research states that,* "...the
>> secondary of a current transformer should not be disconnected from its
>> burden while current is in the primary, as the secondary will attempt to
>> continue driving current into an effective infinite impedance potentially
>> generating high voltages and thus compromising operator safety."  *This begs
>> the question how I can use my DMM clamp meter w/o causing damage or is the
>> italicized text related to very high current applications from the world of
>> medium and high voltage equipment and not as pertinent to the residential
>> and light commercial world I work in?
>>
>> I suspect this is a no-brainer answer for the seasoned professionals on
>> the list and I'll be most appreciative for any proof (no matter how brief)
>> you wish to share.  Ultimately we wish to minimize the need to perform
>> power shut downs and interrupt client service when installing load
>> monitoring CTs to a home but only wish to do so if it is part of a safe and
>> non equipment-harming process.
>>
>> Sincerely,
>> Sam Haraldson
>>
>> [image: OnSite Energy]
>> <https://www.google.com/url?q=https://onsiteenergyinc.com/&source=gmail-html&ust=1677085494759000&usg=AOvVaw2NN36GoM1sjnS4RdC8Svt->
>>
>> SAM HARALDSON
>> Field Operations Director
>> (406) 551-6135
>> 1515 N. Rouse Ave Bozeman, MT 59715
>> Locally owned and operated since 2012
>> [image: B Corporation]
>> <https://www.google.com/url?q=https://onsiteenergyinc.com/bcorp&source=gmail-html&ust=1677085494759000&usg=AOvVaw0EluC1lXtz2KlRFag-htKe>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to