Just spent yesterday debugging a Sol-Ark 15 kW inverter phantom load weirdness.
With Work Mode set at Limited Power To Home it seemed to get a bit schizo, 
pulling around 6kW in from the grid on leg L1 and around 13 kW on the other L2 
leg, with 7kW of PV added. No house loads were involved. The monitoring called 
this a 13 kW load.
I measured something like 50 amps on L2 and neutral; 120 Volts on L1 and 125 
Volts on L2 at the house. My Fluke clamp-on amp meter does not say which way AC 
current is flowing. The utility meter showed it as  power coming in.
At the main meter panel about 150 ft away from the house the voltages were 
better balanced; probably due to proximity to the utility transformer. Those 
leg voltages were balanced when the inverter was shut down.
Oddly, this phantom loading decreased with decreasing PV production later in 
the day.
Working with Sol-Ark tech support we (of course) downloaded new firmware, then 
changed Work Mode to Limited Power To Load. After a couple of resets this had 
the effect of allowing the inverter to cover just the loads in the 
battery-backed subpanel; not those at the house main panel where the CT sensors 
are located. The phantom 13kW load has not recurred.
Has anyone seen an inverter try to mix import and export on different legs by 
creating phantom loads?

Don Barch
Energy Solar



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to