Wrenches, Looking for some guidance on setbacks at ridge for PV systems. The 2018 code states the following:
R324.6.2 Setback at ridge. For photovoltaic arrays occupying not more than 33 percent of the plan view total roof area, not less than an 18-inch (457 mm) clear setback is required on both sides of a horizontal ridge. For photovoltaic arrays occupying more than 33 percent of the plan view total roof area, not less than a 36-inch (914 mm) clear setback is required on both sides of a horizontal ridge. In reading this <https://ipsunsolar.com/new-fire-code-setbacks-in-virginia-will-limit-the-size-of-solar-projects/>article put out by Ipsun Solar regarding the setbacks, they state that if there’s no PV on the opposite side of the roof no setback is required, although their diagram shows a 12” setback. I don’t see any exceptions in the code that indicate that. What’re you all doing for ridge setbacks? Thanks, rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com Roanoke, VA Office: 540.235.3095 Mobile: 540.808.9502 VA Class A Contractor Lic# 2705147660 VA Master Electrician Lic# 2710062762 VA Alternative Energy Systems Installer NABCEP Certified PV Installation Professional 110112-21 
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org