If I am not mistaken, this derives from some UL testing that showed that a 
metal roof may become energized during a thermal event.I suppose no less 
important than our RSD requirements...-GlennSent from my 'smart'phone, so 
please excuse typos and spelling errors.------ Original message------From: 
Jason Szumlanski via RE-wrenchesDate: Tue, Jun 6, 2023 10:25 AMTo: 
offgridso...@sti.net;RE-wrenches;Cc: Jason Szumlanski;Subject:Re: [RE-wrenches] 
Bonding Metal Roofs Part III'm watching this thread with interest. Is anyone 
aware of any serious injury or property damage caused by an energized metal 
roof, and if so, what were the circumstances? Is bonding metal roofs a solution 
looking for a problem?In response to the ground mount alternative, that isn't 
really an option in many areas of Florida where the cost can be 50% higher or 
more to ground mount if it's even practical due to flood level. Tile and 
shingle roofs in Southwest Florida are being switched to metal at shocking 
rates in the wak
 e
 of Hurricane Ian, and we love it from an installer's standpoint. Fortunately, 
I haven't run into any bonding inspection issues for over 10 years here.Jason 
SzumlanskiPrincipal Solar Designer | Florida Solar Design GroupNABCEP Certified 
Solar Professional (PVIP)Florida State Certified Solar Contractor CVC56956On 
Mon, Jun 5, 2023 at 8:28 PM Dave Angelini Offgrid Solar via RE-wrenches 
<re-wrenches@lists.re-wrenches.org> wrote:
Hey Adam,
 
Creative solution #1  Do not install solar on any roof if you can ground mount 
it.
 
Is this He Adam or the Him Adam?
 
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060


On 2023-06-05 3:47 pm, AE Solar via RE-wrenches wrote:


Hey all,
I had started a thread about bonding to metal roofs in 2018 but can't figure 
out how to respond via the archive. I know some things have changed since then, 
so I'm circling back and starting a new thread. 
 
In NY one of our
 inspection agencies (NYSERDA) requires bonding of metal roof panels below the 
array, as well as within a 3' perimeter of the array. S-5! in combination with 
Ironridge is now listed to bond the roof under the array (so long as you hit 
every pan with an attachment) but this doesn't solve the problem of trying to 
bond within the 3' perimeter. For installs where we are only 18" from the 
ridge, this means we are required to bond the adjacent roof as well.
 
Whenever possible we install Illsco SGB-4 lugs under the ridge cap. But more 
and more we're finding roofs where the ridge cap feels inaccessible, tricky, or 
where we simply don't want to get into roof warranty issues associated with 
opening up a prior contractor's work.
 
Wondering if anyone else is coming up against this and what some possible 
creative solutions might be. I don't want to walk away from potential projects 
but...
 
As always, thanks for any thoughts
Adam
 








Adam Katzman (he/him)Autonomous Energies |
 Owner/Operator
www.AutonomousEnergies.com(518) 567-1468


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to