Wouldn't the microinverters shut down if the voltage rose?  They wouldn't be able to raise voltage about PUC/DPU limits I would think. They would shut down on high voltage. I am saying this because of an experience this fall where our infamous Block Island Power Company raised the taps on a local xfmr due to their "secret heat pump program" that was dragging down local voltage. They claimed solar was a burden, but were quiet on the load building program they embarked upon without any disclosure.   When the cooling loads disappeared, the voltage went above our grid tied systems set points and they shut down.  We told the utility they had a high voltage problem and they adjusted the taps.  Of course they did not acknowledge or thank us.  It seems our little coop which is now head from a guy from the Vermont Electric Coop is taking an old utility approach instead of cooperation, integration and maximization of performance and economics.

I'd think you be able to ask how the supply can raise the voltage when there is so much diversified load on the same device.   Electricians have to do a diversity calculation, and I know a utility has to conduct them as part of these studies. Worse case of no load and all generation is such a low probability that to design for it, when/if it occurred, is not a danger and of no material consequence makes little sense. But, we've been dealing with that ever since this person arrived in our neck of the woods.


Chris Warfel



On 12/25/2022 5:21 PM, Garrison via RE-wrenches wrote:
Hi William,

One possible path forward would be to ask the utility co what AC inverter capacity would be allowed. Maybe the solution would be to unplug a micro or two if you are just over the limit. Even better, maybe they would allow you set an export limit on the micros you have installed.

I had a recent situation where a 40kW DC system had exceeded a utility transformer by only 2kW AC, so a simple redesign avoided an $8k invoice from the utility. The utility was not transparent about this option at first and only made it clear after some persistence.

Good luck,

Garrison Riegel
Celestar Solar

On Dec 25, 2022, at 3:14 PM, Darryl Thayer via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:


It is common practice for the utility to overload the transformer a lot for the potential load.  They expect no one will use their service at maximum, furthermore, they expect non coincidence of loads.  Look at the transformer most have a label as to the kW or the unit, and the utility should give you that number along with the impedance.  Note I have had area engineers not understand that solar reduces the load on the transformer.  They have two concerns, you will overload and you will raise the voltage to other customers.  Overload is ridiculous; the transformer must be at least 20 kW if a 15 kW concern is valid.  However, raising the voltage is not.  If all the customers shut off their power, the voltage would rise to the inverter limit,and/or feed current back on the distribution line raising up/downstream customers voltage.  I have had this problem, on three occasions discussions with the utility upper engineering, not local engineer, i prevailed, one case I did not.   In one cast utility allowed connection and put a voltage monitor on secondary voltage, then later allowed permanent connection..   Good luck

On Sun, Dec 25, 2022 at 1:16 PM William Miller via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:

    Wrenched:

    Merry Christmas to those of you that observe such traditions, or
    substitute the winter festivity of your choice.

    I helped a previous employee install an Enphase IQ8 system on his
    home.  He applied for the utility approval concurrently with his
    building permit  The day he got his final inspection the utility
    contacted him and claimed "The aggregate generation exceeds the
    identified transformer rating" and refused him a Permission to
    Operate letter.

    Adding up the service ratings of the homes on his secondary we
    get about 336 kW of potential consumption.  Adding the grid-tied
    systems on his secondary we get about 16.5 kW.  How is it that
    the back-feed exceeds the transformer rating?

    I would appreciate any insight on how to consider this situation
    and how to fight it.

    Sincerely,

    William Miller

    Miller Solar

    17395 Oak Road, Atascadero, CA 93422

    805-438-5600

    www.millersolar.com <http://www.millersolar.com/>

    CA Lic. 773985

    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: RE-wrenches@lists.re-wrenches.org

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

BEGIN:VCARD
VERSION:4.0
N:Warfel;Christopher;;;
TEL;VALUE=TEXT:401-447-5773 (c)
NOTE:Use the cell phone number for all communications.  Thank you.
URL:https://www.entech-engineering.com
END:VCARD
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to