Hey Brad and All,

We've been switching (pun intended:)) from SQ D HU361s to IMO DC Isolators <https://www.imopc.com/products/10000000> with good results.  They make 2,3,4,5,6,8 pole units and that lends itself well to actually switching both poles at reasonable cost.

As for the RSS discussion. I'm hearing some others imply that if "any" DC circuits from a ground mount are on or in a building that the whole array needs RSS?  I don't believe that's what the code intends at all and is certainly uncalled for from any safety standpoint.

We've had many inspectors okay a simple PV Disconnect on the DC side of a ground mount - either on the house or even at the array - as the RSS for DC lines if they do then enter a building - so simply putting an RSS sticker on the DC PV disconnect before it enters the building - end of story.  That's our common practice on ground mounts.

Hope that helps!

Best,

Jeff




Bradley Bassett <mailto:bbasse...@gmail.com>
February 1, 2022 at 2:14 PM
"A switch, outside of the building, opening the PV circuit to the power electronics, and functioning as the pv system disco and the rapid shutdown initiation device, should be all that is required."

That is what I have found most inspectors will accept, but not all. A strict reading of the code does come to the same conclusion that William comes to, and some inspectors will require that. The code is not very specific on where the PV system disconnect should go. It seems to be mostly accepted to be on the PV side of the charge control, but when I read the code strictly it seems to me it should be on the battery side of the charge control since it is only a PV device. Fortunately the PV side is more accepted because that makes things much easier.

What I'm still having trouble with is the requirement for breaking both pos and neg legs in the PV system disconnect unless solidly grounded which most systems are not (690.13(E)). I see that most installers do not break both poles, but only the positive leg, which is of course easier and less expensive. I've quoted the use of dual pole breakers when possible, but OutBack does not really call for that always, and if you ask about their 2 pole 300V breakers they (and Carling) don't say they can be used that way. And if you do, you have to run the wires in opposite directions for polarity. I've asked for clarification but have not received it yet. Then there are the high voltage charge controls like Schneider, where often one uses the SqD HU361, which can be wired in various ways to meet the 600V requirement. It can be wired one pole for up to 18A Isc for PV, or up to 30A if two poles in series, or one pos and one neg pole in the circuit. The Schneider RS Disco does break both poles, one of the few devices that make it clear. I'm curious what others are doing.

Brad



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Brian Mehalic <mailto:br...@solarenergy.org>
February 1, 2022 at 11:23 AM
Sorry, forgot to state my previous comment was in regards to a ground-mount.

Brian



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

William Miller <mailto:will...@millersolar.com>
February 1, 2022 at 10:24 AM

Ray:

Thanks for that input.  I was hoping I was wrong.  I looked for that discussion in the archives but could not find it.

William

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com <http://www.millersolar.com/>

CA Lic. 773985

*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Ray
*Sent:* Tuesday, February 1, 2022 10:11 AM
*To:* re-wrenches@lists.re-wrenches.org <mailto:re-wrenches@lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems

 Ground mounts do NOT require RSS.  We hashed this out years ago on the Wrenches list, when NEC 2017 came out.

See Figure 690.1(B) Note (2): /" The PV system disconnect in these diagrams separates the PV system from all other systems"./

Thus, the PV disconnect is defined as the transition point from the PV system to all other systems, like battery or inverter systems. The installer/ designer decides where to put that disconnect.  I usually put it on the wall before it goes into the building, and I have never had an inspector question that.

Thanks,

Ray Walters
Remote Solar
303 505-8760

On 2/1/22 10:06 AM, William Miller wrote:



_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to