Hey Brad and All,
We've been switching (pun intended:)) from SQ D HU361s to IMO DC
Isolators <https://www.imopc.com/products/10000000>
with good results. They make 2,3,4,5,6,8 pole units and that lends
itself well to actually switching both poles at reasonable cost.
As for the RSS discussion. I'm hearing some others imply that if "any"
DC circuits from a ground mount are on or in a building that the whole
array needs RSS? I don't believe that's what the code intends at all
and is certainly uncalled for from any safety standpoint.
We've had many inspectors okay a simple PV Disconnect on the DC side of
a ground mount - either on the house or even at the array - as the RSS
for DC lines if they do then enter a building - so simply putting an RSS
sticker on the DC PV disconnect before it enters the building - end of
story. That's our common practice on ground mounts.
Hope that helps!
Best,
Jeff
Bradley Bassett <mailto:bbasse...@gmail.com>
February 1, 2022 at 2:14 PM
"A switch, outside of the building, opening the PV circuit to the
power electronics, and functioning as the pv system disco and the
rapid shutdown initiation device, should be all that is required."
That is what I have found most inspectors will accept, but not all. A
strict reading of the code does come to the same conclusion that
William comes to, and some inspectors will require that. The code is
not very specific on where the PV system disconnect should go. It
seems to be mostly accepted to be on the PV side of the charge
control, but when I read the code strictly it seems to me it should be
on the battery side of the charge control since it is only a PV
device. Fortunately the PV side is more accepted because that makes
things much easier.
What I'm still having trouble with is the requirement for
breaking both pos and neg legs in the PV system disconnect unless
solidly grounded which most systems are not (690.13(E)). I see that
most installers do not break both poles, but only the positive leg,
which is of course easier and less expensive. I've quoted the use of
dual pole breakers when possible, but OutBack does not really call for
that always, and if you ask about their 2 pole 300V breakers they (and
Carling) don't say they can be used that way. And if you do, you
have to run the wires in opposite directions for polarity. I've asked
for clarification but have not received it yet. Then there are the
high voltage charge controls like Schneider, where often one uses the
SqD HU361, which can be wired in various ways to meet the 600V
requirement. It can be wired one pole for up to 18A Isc for PV, or up
to 30A if two poles in series, or one pos and one neg pole in the
circuit. The Schneider RS Disco does break both poles, one of the few
devices that make it clear. I'm curious what others are doing.
Brad
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Brian Mehalic <mailto:br...@solarenergy.org>
February 1, 2022 at 11:23 AM
Sorry, forgot to state my previous comment was in regards to a
ground-mount.
Brian
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
William Miller <mailto:will...@millersolar.com>
February 1, 2022 at 10:24 AM
Ray:
Thanks for that input. I was hoping I was wrong. I looked for that
discussion in the archives but could not find it.
William
Miller Solar
17395 Oak Road, Atascadero, CA 93422
805-438-5600
www.millersolar.com <http://www.millersolar.com/>
CA Lic. 773985
*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] *On Behalf Of *Ray
*Sent:* Tuesday, February 1, 2022 10:11 AM
*To:* re-wrenches@lists.re-wrenches.org
<mailto:re-wrenches@lists.re-wrenches.org>
*Subject:* Re: [RE-wrenches] Rapid Shutdown for Off-grid systems
Ground mounts do NOT require RSS. We hashed this out years ago on
the Wrenches list, when NEC 2017 came out.
See Figure 690.1(B) Note (2): /" The PV system disconnect in these
diagrams separates the PV system from all other systems"./
Thus, the PV disconnect is defined as the transition point from the PV
system to all other systems, like battery or inverter systems. The
installer/ designer decides where to put that disconnect. I usually
put it on the wall before it goes into the building, and I have never
had an inspector question that.
Thanks,
Ray Walters
Remote Solar
303 505-8760
On 2/1/22 10:06 AM, William Miller wrote:
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org