I have a system where the SE10000 inverter fried internally. The 60A AC output 
breaker tripped several times, as a result of the homeowner resetting over and 
over until he called me.
I replaced the inverter under warranty and all is fine, except on sunny days 
the breaker will trip at about 40A, close to the max output of the inverter. 
Reset it outside of peak inverter output and its good. I assume the breaker has 
weakened from stress of some sort, so I replaced it and time will tell.
Anyone ever seen a breaker have it's trip point reduced like this?


Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar]
Owner|Principal, VT Solar, LLC
Celebrating our 30th Anniversary 1991-2021!!
www.vermont.solar 
[https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0]
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to