Hi Corey,

I start off by using the BSTC value as the baseline Isc before I do the
classic 1.25x1.25 multiplication.  It does end up causing larger currents
and oversizing the wire. Most of the time our projects have a strict DC
Vdrop requirement so we're always oversizing the wire anyway, so it's not a
big deal.  However, for the Neher-McGrath calculations, I will typically
run a SAM model and re-calculate the ISC that way (on 100kW and larger
projects only).  I base this off the SolarPro article from a few years back
where you calculate Isc0 using nameplate Isc, cell temperature, irradiance,
and the module current coefficient.  For the irradiance, I use the front
side POA and the anti-POA multiplied by the bifaciality factor - usually
70%.

My last run had a situation where SAM was calculating a higher Isc value
than the Isc0 equation value, so I will probably end up using that.  It is,
however, less than the traditional BSTC nameplate x 1.25 method.

Regards
Steven Lawrence, PE
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to