I think whichever system ( Schneider, OB, sol-ark) it has to include closed 
loop battery communication. 

I really want to try the sol-ark but I won’t until they completely fix their 
small 120v load issue. 

Jay

Peltz Power. 



> On Mar 3, 2021, at 6:30 AM, Dave Tedeyan <dtede...@taitem.com> wrote:
> 
> 
> The Radian is also the system that I would typically use in this situation. 
> Although I am interested what people think about using a Sol-Ark inverter 
> here. I have not used one yet, but I am interested in the fact that 
> everything is integrated into one box, the string voltages can be up to 500V, 
> and also if there is a battery failure at some point they can still run as a 
> grid tied system. 
> Cheers, 
> Dave
> 
> Dave Tedeyan, PE
> Senior Engineer | Taitem Engineering, PC
> 
> 110 South Albany Street | Ithaca, NY 14850
> o. 607.277.1118 x121  f. 607.277.2119
> www.taitem.com
> 
> Solar • Sustainability • Energy • Design
> Certified B-Corporation since 2013
> 
> 
>> On Wed, Mar 3, 2021 at 7:10 AM John Blittersdorf 
>> <john.blittersd...@gmail.com> wrote:
>> William,
>>    I agree with you with Radian, Fortress and just add a subpanel identical 
>> to the main grid panel as close possible. Put all critical loads on sub and 
>> larger loads on grid panel.  Being side by side, swapping circuits is easy. 
>> I also install an iota charger for generator redundancy. OpticRE works great 
>> for monitoring.  
>> 
>> John Blittersdorf
>> 
>>> On Wed, Mar 3, 2021 at 1:19 AM William Miller <will...@millersolar.com> 
>>> wrote:
>>> Friends:
>>> 
>>>  
>>> 
>>> I am getting asked more often to provide design for grid-tied battery 
>>> backup systems.  I generally try to talk clients out of battery backup 
>>> because I have always felt that the grid is the greenest battery and that 
>>> the grid reliability is better than one might remember.  However, with 
>>> climate change and media attention, the need and market pressure is 
>>> becoming stronger.
>>> 
>>>  
>>> 
>>> I am really interested in what others have created in the way of solutions 
>>> to this question.  I have thought about it a lot.  If its ok, I’d like to 
>>> free-associate about some of my concerns and conclusions then ask if any of 
>>> you are willing to share your ideas on how best to fill this need.  Here 
>>> goes:
>>> 
>>>  
>>> 
>>> I am a firm believer in segregate load delivery for these reasons:
>>> 
>>> 1.   To back up an entire grid service you have to, in good conscience, 
>>> perform a thorough load study and provide enough through-transfer to 
>>> provide for maximum load conditions during grid up-time.  The backup system 
>>> cannot be a supply bottle-neck.
>>> 
>>> 2.   I don’t accept manual load-shedding for one moment.  What if the AC 
>>> and the dryer are running when the grid goes out?  The system crashes.
>>> 
>>> 3.   In a home with whole-house backup, it is difficult for the consumer to 
>>> know there is an outage and to conserve.  Cellphone notification features 
>>> are now more common, but cell phone batteries die and phones get left in 
>>> the other room with the ringer off, so it is possible for homeowners to 
>>> leave consumptive loads on after the grid goes down.
>>> 
>>>  
>>> 
>>> Conclusion:  With segregated loads, the transfer, inverter and storage can 
>>> be scaled down and the reliability increases.  Less cost, better 
>>> performance.
>>> 
>>>  
>>> 
>>> So given that the system sizing will be modest, has anyone come up with a 
>>> reasonable design using standard, grid-sell capable battery inverters?
>>> 
>>>  
>>> 
>>> Here is how I am imagining such a system:
>>> 
>>>  
>>> 
>>> I see a modest battery system with a 4 to 8 KW inverter, DC coupled PV and 
>>> a matching no-maintenance battery system. It would have these components:
>>> 
>>>  
>>> 
>>> Inverter:  Must have a dedicated generator and grid input and good remote 
>>> monitoring,  robust web interface and email notification.  Outback Radian.
>>> 
>>>  
>>> 
>>> Batteries:  Gel or lithium.  I have a client that has been grid-floating a 
>>> set of MK Powered gel batteries since 1999.  Or a Blue Planet or Fortress 
>>> cabineted system.
>>> 
>>>  
>>> 
>>> Generator:  Small pad-mount natural gas or propane fueled generator or a 
>>> portable gas powered unit with stabilized gas.  If the generator is 
>>> portable, provide an AC flanged inlet and sturdy cord long enough so 
>>> generator can be 10 feet from any opening in the home.  Provide durable 
>>> signage on the generator indicating CO safety practices.
>>> 
>>>  
>>> 
>>> PV: DC coupled for simplicity.  Sized based on annual energy needs, not on 
>>> critical loads.  Grid power is likely to go down in the stormy winter 
>>> months or smoky fire season, so PV is not a reliable energy source during 
>>> grid outages.
>>> 
>>>  
>>> 
>>> AC Distribution:  Segregated loads with at least one commonly used lighting 
>>> circuit not on the critical loads panel so the homeowner soon realizes the 
>>> power is out.
>>> 
>>>  
>>> 
>>> Unless you are a Tesla dealer, I am sure many of you have gone through the 
>>> same mental acrobatics trying to figure out the best solution to this 
>>> design request.  I am very interested in what the rest of you may have come 
>>> up with.
>>> 
>>>  
>>> 
>>> Thanks in advance.
>>> 
>>>  
>>> 
>>> William Miller
>>> 
>>>  
>>> 
>>> Miller Solar
>>> 
>>> 17395 Oak Road, Atascadero, CA 93422
>>> 
>>> 805-438-5600
>>> 
>>> www.millersolar.com
>>> 
>>> CA Lic. 773985
>>> 
>>>  
>>> 
>>>  
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to