Wrenches,


You can have 4800W on L1 and 0W on L2. It has huge 240V peak power. But you are 
correct that some 120V inductive loads >3/4hp can be an issue. We recommend 
rewiring those massive motors to 240V (most are convertible on the motor). The 
1400W limit is with DC Loads. A heat gun on high is an AC load but on low, it 
only uses 1/2 of the sinewave (DC load). Our limit for DC loads (hair dryer, 
leaf blower, drill, blender, curling iron, heat gun only on low setting) is 
1400W.


Thank you and have a blessed day,

Dustin Douglas

Engineering Support Lead

(972)575-8875 ext. 108

http://www.Sol-Ark.com









---- On Tue, 09 Feb 2021 23:23:22 -0600 Nick A Lucchese <luccheseso...@me.com> 
wrote ----


I agree with many of you on waiting awhile longer until these issues are sorted 
out. While I definitely think there is plenty of room beyond our usual 
favorites for another robust battery based inverter to offer I don’t intend to 
embark on another frustrating adventure at mostly my expense. At this point I’m 
more excited for the Midnite inverters more than anything and know once they’re 
released I won’t feel like I made a mistake. Meanwhile I’ll definitely be 
sending wishes of success to Sol-Ark. I’ve heard a lot of good things and will 
remain optimistic and hopeful it’s shortcomings will be resolved soon without 
needing to stack multiple units or a transformer.

Nick A Lucchese

On Feb 9, 2021, at 12:17 PM, Dave Angelini Offgrid Solar 
<mailto:offgridso...@sti.net> wrote:


Yes that has happened with 2 of mine Jerry.  I like the Transformer Devils that 
I know. Might check these out in 2 or 3 years. The whole all in one does not 
really appeal to me either but I will keep an open mind, in 2 or 3 years! 

 

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  mailto:offgridso...@sti.net
text 209 813 0060


On Tue, 9 Feb 2021 10:19:44 -0800, Jerry Shafer 
<mailto:jerrysgarag...@gmail.com> wrote:

It is also interesting how sol ark sells over the counter to end users and also 
through distributors but at nearly the same price so it makes it difficult for 
our distributors to carry the sol ark products. Jerry



On Tue, Feb 9, 2021, 7:42 AM Jay <mailto:jay.pe...@gmail.com> wrote:

It is odd that the 12kw 20kw surge sol ark can't run a 15 amp 120v air 
compressor
 
 I saw a you tube video from what appears to be a pretty well versed installer 
who mentioned that sol ark knows this is an issue and specifically mentioned 
that his small air compressor will shut his 12kw inverter down. He didn't 
mention if there is a fix coming. 
 
 I guess I'll wait to buy one until they have that issue sorted out. 
 
 Jay
 
 Peltz power. 
 
 
 
 
 _______________________________________________
 List sponsored by Redwood Alliance
 
 List Address: mailto:RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 There are two list archives for searching. When one doesn't work, try the 
other:
 https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules & etiquette:
 http://www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 http://www.members.re-wrenches.org/



_______________________________________________
List sponsored by Redwood Alliance

List Address: mailto:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org







_______________________________________________ 
List sponsored by Redwood Alliance 
 
List Address: RE-wrenches@lists.re-wrenches.org 
 
Change listserver email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 
There are two list archives for searching. When one doesn't work, try the 
other: 
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
 
List rules & etiquette: 
http://www.re-wrenches.org/etiquette.htm 
 
Check out or update participant bios: 
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to