Kris,

Are they telling you the problem is the connection in the meter base?  We get 
this all the time from local utilities.  Even with the listed Milbanks like you 
describe, they say no and direct us to tap on the load side of the meter base.  
I agree that you may consider an informal complaint with your PSC.  Our KY PSC 
denied my complaint but promptly initiated a state-wide hearing on 
interconnection standards.

Good luck.

Matt



From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
Christopher Warfel
Sent: Wednesday, October 28, 2020 6:48 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Supply side denial


I would think that would be illegal.  They don't have jurisdiction on supply 
side taps. It's past the meter, and expressly allowed in the NEC.  I would 
definitely first ask to talk to a higher level person than the one denying it 
(paper trail important). If that does not work, then the PSC is your best 
option.  Chris
On 10/27/2020 6:27 PM, Kristopher Schmid wrote:
Hi All,

I have a utility that is hinting that they are going to deny my interconnection 
application with a supply side connection and require a load side.  Has anyone 
seen this before?

(Proposed interconnection would be with Milbank step lugs in a 200 A socket and 
a 60 A fused disconnect within 10 feet.)

If they refuse it, i am thinking that registering a complaint with the 
Wisconsin PSC may be appropriate.

Kris


Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE



_______________________________________________

List sponsored by Redwood Alliance



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



There are two list archives for searching. When one doesn't work, try the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

http://www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to