Hi Don

I’m pretty sure the only option for a vfd is a 3 phase motor on that pump. The 
advantage would be complete adjustability as to how fast/slow it starts. 

Another option would be the Grundfos sq pump which is a soft start pump. It’s 
not going to be adjustable. 

But I’d like to know if there are soft start options for single phase 240vac 
motors. 

Jay

Peltz power. 


> On Oct 15, 2020, at 12:42 PM, d...@energysolarnow.com wrote:
> 
> 
> With help and a site visit from Adam of Enphase tech support this Ensemble 
> system was successfully brought through commissioning. We had to do a battery 
> black start after it discharged over the weekend.
> However, functional testing brought up another issue-- in off grid mode the 
> well pump consistently kicks off the two Encharge3 batteries, presumably from 
> inrush current. This is a 3/4 Franklin pump that apparently lacks any 
> capacitor soft start. It is on a 20 amp 2-pole breaker. We measured the 
> operating current at something like 6 amps; the inrush current is likely a 
> multiple of that. The soft starters from Hyper Engineering recommended by 
> Enphase are made for HVAC units with more accessible wires for compressor and 
> fan. This well pump has only two wires.
> Can anyone recommend a soft starter or variable frequency drive (VFD) starter 
> for a two-wire well pump?
> 
> Thanks
> Don Barch
> Energy Solar
> -------- Original Message --------
> 
> Date: Thu, 1 Oct 2020 18:12:39 -0700
> From: Louis Woofenden <lo...@woofenden.net>
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Commissioning issues with Enphase Ensemble
> Message-ID: <12123009-ea4a-ffdc-f927-8e0ac3891...@woofenden.net>
> Content-Type: text/plain; charset="utf-8"; Format="flowed"
> 
> 
> Hi Don and Wrenches,
> 
> I have commissioned four new Ensemble systems over the past two weeks. 
> All storage additions to existing PV systems with Enphase 
> microinverters. Although there are parts of the process that are a bit 
> clunky, we have not had the problems you mention. I followed the 
> instructions in the tech brief "Ensemble Commissioning via Installer 
> Toolkit 3.0," linked at 
> https://enphase.com/en-us/certification-support-program-guidelines 
> (direct link to the PDF is 
> https://enphase.com/sites/default/files/Tech%20Brief%20-%20Ensemble%20Commissioning%20via%20Installer%20Toolkit%203.0.pdf).
> 
> My experience is that each of the four Enpower microgrid interconnection 
> devices we've installed started up in passthrough mode, so if input 
> breakers are on in the MID, backup loads have had power before 
> commissioning is completed, and power has remained on for those backup 
> loads even after we turned off the PV and ESS disconnects to wait for 
> utility PTO after doing commissioning and functional testing.
> 
> It did take us some time to do the Envoy software update before 
> commissioning, and the system does require a second trip for functional 
> testing after the Encharge battery software updates have been done (up 
> to 12 hours). I haven't stuck on site for the Encharge/Enpower software 
> updates, but it looks like they are taking 4-6 hours for us, based on 
> percentage done by the time I've left the site (system sizes from 10.08 
> kWh to 20.16 kWh). Yeah, it's a second trip. I've used the trip to meet 
> with electrical inspectors for these first systems.
> 
> One "trick" I've used on the Envoy software update is that you once you 
> scan in the serial numbers of each Enpower & Encharge with the installer 
> toolkit and plug in the cell modem and wireless communications kit, the 
> installer toolkit will allow the Envoy software update to work, and you 
> can get it taken care of early in the day, while still hanging boxes, 
> running conduit, etc.
> 
> I would agree that there are definitely parts of the new installer 
> toolkit that aren't intuitive. I missed the "edit" button on the devices 
> page for a bit (which is not mentioned in the tech brief), and couldn't 
> figure out how to increase the device count, for example. I also had to 
> try the Envoy update twice for some of these systems, as it threw an 
> error code the first time around, so for some of the systems it took 
> closer to 45-50 minutes to get the Envoy software update done.
> 
> Hope the next one goes more smoothly for you! New products, new 
> challenges, I guess.
> 
> Best,
> 
> Louis Woofenden
> 
> d...@energysolarnow.com wrote on 9/30/20 2:59 PM:
> > Wrenches-
> > I'm having a lot of difficulty commissioning my first Enphase Ensemble 
> > installation. This is on a pre-existing microinverter installation. 
> > Have been on the phone with tech support several times; each time they 
> > forward a Tech Brief about commissioning that has different and 
> > slightly conflicting instructions. It seems the order of turning on 
> > each box is critical. Because of already-obsolete software that they 
> > ship with, the software must be updated before activating the Envoy, 
> > Enpower, and Encharge or they will not work.
> > And for some reason the Envoy must have both Wifi and cell connection 
> > before even starting commissioning, but the slower cell connection is 
> > used for software download so it takes up to 12 hours.
> > This commissioning must be done on-site using their latest version of 
> > Installer Toolkit on a smart phone. Sure, there are buttons in 
> > Enlighten's Activation page to add an Enpower and Encharge, but these 
> > do not work "yet".
> > Enphase tech support says they are working on making this a single-day 
> > process rather than the current multi-day commissioning. This does not 
> > even count the actual hardware installation time.
> >
> > I would advise anyone against moving any loads to a new subpanel 
> > before the entire system is commissioned and operating.
> > As of now I have an Enpower that mistakenly thinks it is off-grid when 
> > the grid is present, so it has told the Envoy to shut down the PV 
> > microinverters and batteries. These are relay controlled, therefore it 
> > is not possible to have them connected without software control.? It 
> > has already committed the major crime of shutting down the backed-up 
> > loads while the grid is still present. Enphase is working on it, but 
> > seem to be developing software on the fly. I suppose their integration 
> > process has been hit hard by pandemic distancing, and they are all 
> > working remotely.
> >
> > Has anyone else had a successful experience commissioning an Ensemble?
> > I'd like to hear about the doos-and-don'ts.
> >
> > Don Barch
> > d...@energysolarnow.com <mailto:d...@energysolarnow.com>
> > 
> --
> Louis Woofenden
> Engineering Director
> Net Zero Solar, LLC
> 101. W. 5th St., Tucson, AZ 85705
> Arizona ROC #248710, 259756, 259521
> 
> Phone:520.207.4053 <tel:520.207.4053>Ex. 3
> Cell:520.237.5040 <tel:520.237.5040>
> Fax:520.203.7230 <tel:520.203.7230>
> 
> NABCEP Certified PV Installation Professional
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to