Don't just nag on Outback. It's the same issue with the Schneider Electric XW distribution panel and with the Midnite E-panels.

Kent Osterberg
Blue Mountain Solar

On 9/13/2020 1:10 PM, Ray wrote:
I'm taking a Mike Holt course on NEC 2020 changes for my license renewal, and I just came across these changes in 408.18.  They apply to Switchboards and Switch gear, which the Outback GS Load center qualifies as.  The new requirements do not allow arrangements that require the installer to reach across uninsulated, ungrounded terminals or busses in order to make connections.

As has been brought up on this list before, the GS load center is a nightmare to work in, with the main shunt, negative buss, and ground buss buried behind layers of other equipment, including both ungrounded AC and DC  exposed breaker terminals.

I'm pretty sure they added this new code section to address equipment just like this.  Outback? are you finally going to fix this, and give us a better load center to work with?