Dave –
Related but different.

CA Rule 21 and HECO Rule 14H and NE-ISO require equipment tested to UL1741 SA 
(which outlines what additional functions beyond UL1741 inverters must be 
capable of) utilizing the appropriate utility Source Requirement Document 
(SRD).  The SRD spells out which UL 1741 SA additional functions  -with set 
point values-  each utility wants enabled .  This allows for “smart inverter” 
functionality to prevent undesirable behavior.

The objective of the IEEE 1547.x updates is to harmonize testing across the 
industry to provide a uniform baseline for “smart” inverter 
functionality/capability.  I believe there will still be specific SRDs – that 
is, not all tested IEEE 1547-2018 functionality will be enabled by default.

I vaguely remember hearing of deadline for certification being at most 18 
months after publishing of the standard (which I think means the 
IEEE1547.1-2020 standard as that actually outlined the testing procedures for 
listing), which would very roughly be Jan 2022.

Also, I think “Hawaii” is being very aggressive with this deadline  – I think 
they (HECO?  HELCO? Other?) have set July 1, 2021 as testing deadline?  Anyone 
have more details?

Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: https://solaracademy.sma.de/en.html

SMA America Solar Academy webinars: https://solaracademy.sma.de/en/courses.html
Choose "United States"
[A picture containing drawing, food  Description automatically 
generated]<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-america.com%2FShadeFix&data=02%7C01%7CMichael.Mahon%40sma-america.com%7Ceb737bd7586646b4d14b08d811405661%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637278315315432372&sdata=uyZ5K7ayyl6y%2Fa90qQ0%2F4r8WSV0PYLK1CYMJQxPVeCQ%3D&reserved=0>

[Linkedin Logo]<http://www.linkedin.com/company/364675> 
[cid:image003.jpg@01D67C53.80A512C0] 
<http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] 
<http://smaadvance.com/signup/>  Follow, Like, Share

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Dave 
Angelini Offgrid Solar
Sent: Thursday, August 27, 2020 8:19 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Stackable Battery-Based systems complying to IEEE 
1547-2018 standard


Is IEEE 1547.1-2020 related to the issue in Hawaii  (HEICO) too much solar and 
cloud events that cause the transients? RULE 21 in California kind of thing? 
Or, it it different please?



Dave Angelini Offgrid Solar

"we go where powerlines don't"

http://members.sti.net/offgridsolar/<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Cef932f50809b4d60b19408d84a943173%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637341347646941703&sdata=LMUx5jH6uRLvC6bNDqTN1oBIRg6tZZzpJdn5js0VYbY%3D&reserved=0>

e-mail  offgridso...@sti.net<mailto:offgridso...@sti.net>

text 209 813 0060


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to