I've used it a few times for battery and inverter cables and it works just fine.  It just has a thicker jacket so when you heat shrink it at the lugs, it looks funny.  Not a serious problem, just get a higher ratio heat shrink like 3 to 1, and it should be fine.
Ray Walters
Remote Solar
303 505-8760
On 8/4/20 12:32 PM, Kirk Herander wrote:
Thanks Ray,
I am going to use the 2kva DLO cable. It is dual rated as RHW-2, which is what inverter OEM recommends. AWC warehouse is also close by in PA. also.
On 8/1/2020 8:16:16 PM, Ray <r...@solarray.com> wrote:

I would look at Diesel Locomotive Cable  DLO, which is usually dual rated RHH/RHW-2 for us non locomotive folks. 2000 v rated.  Its pretty easy to work with, flexible, but has a 2nd inner liner that gives it the higher volt rating.  Its also usually tinned conductors too.
https://www.awcwire.com/productspec.aspx?id=dlo

Ray Walters
Remote Solar
303 505-8760
On 8/1/20 7:09 AM, Kirk Herander wrote:
I need to spec battery cable for a nominal 850 vdc LFP bank. Several brands of power cable list their rating at a dual 600/1000v. it is my understanding that to be listed in this manner, the cable must pass a test apply of over 600v for a short period  without breakdown. But under normal operation IMO, the voltage is not to exceed 600v. And this test is done with AC voltage, not DC.
"*UL 1277: Power and Control Tray Cable*

UL 1277, the standard for electrical power and control tray cable, was recently updated, allowing manufacturers with UL approved tray cable to market their product as 600V/1kV rated. To be dual rated, products must use a recognized 1kV rated conductor and pass a higher voltage AC Hipot test on the completed cable. This test requires each insulated conductor in finished cable to withstand a specified voltage range for one minute without breakdown. If a product passes the AC Hipot test, it is suitable for 1kV use."

Am I getting this right? And If so, one should not use this 600/1000v wire if normal operating voltage is above 600v as is my case? Proper rating should be dual 1000/2000v like PV wire?
What do you experienced high voltage battery gurus use in my 
application? Thanks.
_______________________________________________
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to