Are you sure its just the transfer switching causing problems? I've seen quite a bit of lights dimming, flickering, and strangeness with XW inverters ( and many others) just in normal operation.  Certain LEDs are particularly sensitive, just another appliance coming on can cause noticeable flicker that bothers some clients.  Our solution was to try different brands of LEDs till we found ones that had less trouble.  I recall the Phillips ones being good, but you would have to test a few to see.

Ray Walters
Remote Solar
303 505-8760

On 4/21/20 12:26 PM, Jason Szumlanski wrote:
I have not looked into that, but the problem also exists transferring from inverter to generator. The owner wants "clean" power all the time, and just keeping him on inverter power all the time would be a solution.

*

*


On Tue, Apr 21, 2020 at 9:35 AM Tump <t...@swnl.net <mailto:t...@swnl.net>> wrote:

    Have you shortened the transfer time from gen to inv, voltage “cut
    out"acceptance of the gen in power instead of their 90Vac to say
    110V/L ? Raising the output voltage on the 6848s & gen set for
    VD/voltage sag issues under heavy loading? Watch this as sometimes
    under heavy loading it will cut the AC input. I use the config
    tool to address this kind of issue, gives me a bit more control.
     I have a client that has a large external battery charger similar
    to a fork truck unit that he alleges causes "dirty power" while
    the genset is supplying power to the charger, w/o charging thru
    the inverters. Unfortunately w/ the virus I have yet to confirm.
    On Apr 21, 2020, at 8:27 AM, Jason Szumlanski
    <ja...@floridasolardesigngroup.com
    <mailto:ja...@floridasolardesigngroup.com>> wrote:

    I actually need 400Adc at 51V nominal of total charge rate. I was
    hoping to use 100Adc chargers for redundancy, or some combination
    of 2-8 chargers to reach the needed current, assuming they can be
    synced up. I don't think the charging algorithm needs to be
    complicated. We are basically bulk charging the LiPOs to 80% with
    the battery BMS controlling the generator. The concept is to get
    to 80% sometime in the night and solar kicks in during the day to
    reach 100% using 2-stage charging from the XW charge controllers.

    The problem I have is the quad XW6048s in the system run at a
    pretty good load typically... often over 50%. This is off-grid
    with generator backup. The transfer switches in the XW6048 are
    causing surges and brownouts when the switched loads are high,
    especially smart dimmers and televisions. I need seamless power
    for this client. My thought is to abandon the internal chargers
    in the XW6048s and just run loads off inverter power full-time. I
    would charge the batteries with external battery chargers. The
    tricky part is how to adjust the charge rate based on load, and
    also based on solar input. I need to limit the net charging
    current. Of course, I still need 400Adc of charging current,
    which I'm learning might be hard to find. I don't really want to
    buy four more XWs - that's a pretty expensive solution.

    Jason Szumlanski
    Florida Solar Design Group


    On Fri, Apr 17, 2020 at 4:26 PM Dave Angelini Offgrid Solar
    <offgridso...@sti.net <mailto:offgridso...@sti.net>> wrote:

        I use the CSW 4048. It has a 50 amp charger. A good spare for
        clients. Get 2 of them. Repurpose an old Radian or XW well
        over 100A. XW+ is 140adc.

        *Dave Angelini Offgrid Solar*

        *"we go where powerlines don't"
        http://members.sti.net/offgridsolar/
        
<https://mailtrack.io/trace/link/3c165022419c043bf7fae6f8ecf982e3ecc4a1fe?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=465d0580a80dab11>
        e-mail offgridso...@sti.net <mailto:offgridso...@sti.net>
        text 209 813 0060*

        On Fri, 17 Apr 2020 14:21:14 -0400, Jason Szumlanski
        <ja...@floridasolardesigngroup.com
        <mailto:ja...@floridasolardesigngroup.com>> wrote:

        I'm looking for a standalone 51V nominal battery charger
        suitable for a LiPO battery with 2-stage charging and
        adjustable setpoints for max current and battery voltage. It
        would require dual chargers with 100A capacity (I want dual
        chargers for redundancy so I have at least 50% capacity if
        one goes bad). Ideally they would sync up so they change
        stages simultaneously, but I'm not sure if that's really
        important.
        Who makes something like that?
        Jason Szumlanski
        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
        
<https://mailtrack.io/trace/link/87e7eed38e9919757f199821e1f1b51753af3cb1?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5ee8402176433da9>

        List-Archive:
        
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
        
<https://mailtrack.io/trace/link/45aed2d671a970abd91ee83e200e9373ed935a5a?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=2f4f6344e534e2e4>

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        
<https://mailtrack.io/trace/link/e8496866bc61c192fcee0b1de1be878634272fa5?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=b8be63d2aca26404>

        Check out or update participant bios:
        www.members.re-wrenches.org
        
<https://mailtrack.io/trace/link/f0dae2dae01e0e6358327e8e3251cc7837ca6e67?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=38f27b2520ac6e44>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/dd050ae2c673dd4cd802c37bddbe474318a70102?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=f5f844835e29054a>

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<https://mailtrack.io/trace/link/0493368bc16bceab5920aa18b24318090756debd?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=fc66d8aeb73dcca9>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    
<https://mailtrack.io/trace/link/54a0a0a054b3db6f12f95c3d119509afbcc9d907?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1256f8d4cb1cef4b>

    Check out or update participant bios:
    www.members.re-wrenches.org
    
<https://mailtrack.io/trace/link/add324be80479a0f6a3e9ad751810fe121f72acc?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=d2f278a758a9f1f6>


    *t...@swnl.net**www.SWNL.net*
    Solarwinds Northernlights *//*
    */   Serving Mid Coast Maine & Northern California/**/
    /**/ 207-832-7574   Cl. 610-517-8401 /*
    *//**/Blair "TUMP" May/*

    */               ********  MAINE'S CHARTER ********
    /**//**/NABCEP "Certified PV Installer"/**/
    /**/
    ********  MAINE'S CHARTER ********
    /**/        Trace Xantrex "Certified" Dealer / Installer"/*




    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    
<https://mailtrack.io/trace/link/034e10172e75c7776537720aa88742289db096e3?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=5104423cdadb7d6d>

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<https://mailtrack.io/trace/link/e16ea2564076b31906b8100e4de30a434d2af66d?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=c232e6b5f7e80047>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    
<https://mailtrack.io/trace/link/22a970036140dda9b0f56451058bd6a063248e46?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=74f63fd18f433198>

    Check out or update participant bios:
    www.members.re-wrenches.org
    
<https://mailtrack.io/trace/link/18dc5efffc16498bf2b5b6f68a4edbffcefab7ad?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4bf5e6fecf6f36a1>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to