Gigavac.-GlennSent from my 'smart'phone, so please excuse typos and spelling 
errors.------ Original message------From: Chris SparadeoDate: Fri, Nov 22, 2019 
10:47 PMTo: RE-wrenches;Cc: Subject:[RE-wrenches] 600V DC contactorHi 
wrenchers,I am currently on the look out for a DC contactor to suit my needs. A 
little background:Per Sonnen Batterie tech support’s recommendation I have 
installed a 10 kW SolarEdge HD Wave inventer coupled with the Sonnen Eco 12. 
Although the Sonnen Eco 12 uses an Outback Radian 8kW multimode inverter(of 
which Outback suggests to max AC couple input of 5kW) Sonnen says that AC PV 
input greater than 8kW will require a contactor  to interrupt a string or two 
of the grid interactive inverter so that it’s output will remain less than the 
max 8kW input. That’s fine and well, but when asked directly, Sonnen didn’t 
have a part # for the contactor and suggested that anything over 150V DC would 
be difficult to find. Anyone know of a 600V rated contactor that
  would
 suit the bill? Essentially the contactor would need to sense grid interruption 
(via a 15A-AC breaker) and open a 600 V rated DC string. I’ve done some 
preliminary searching and have come up empty handed. Any input would be greatly 
appreciated.Best,Chris -- Chris SparadeoC_802-369-4458H_802-728-3059
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to