There doesn't seem to be a definitive and detailed consensus
article/resource out there that addresses this topic. There are articles
that dance around the subject, but little in terms of practical ways to
accomplish grounding/binding with a supply side interconnection. AHJ's and
engineers have all kinds of differing opinions. As an industry, it seems
like we should have a definitive guide on the subject.

Let's take a simple/common ungrounded inverter (or microinverter) system
that is interconnected using supply side taps inside an existing load
center with main disconnect. From the roof to the PV AC Combiner you have
an appropriately sized EGC, and no GEC because a GEC is not required in
this ungrounded system other than the existing premises GEC (and GE
system). Let's assume the AHJ agrees that no GEC is required from the roof,
which is a whole other subject that drive me nuts). Coming from the PV AC
Combiner panel (if present) or Inverter you have two current carrying
conductors L1 and L2 that are tapped on the service conductors. The neutral
from the PV AC Combiner or inverter is landed on the existing neutral bus
of the same main load center where the tap is made.

Now what happens with the EGC that comes from the roof to the PV AC
Combiner (or inverter)?

What I have run into, and there may be other opinions, are the following
assertions by AHJs:

   - Land the EGC on the PV AC Combiner and stop there. Bond neutral to
   ground. The neutral carries the fault current to the system bonding point
   in the main service panel.
   - Land the EGC in the PV AC Combiner and continue the EGC to the ground
   bar in the main service panel. Do not bond neutral to ground in the PC AC
   Combiner.
   - From the PV AC Combiner, install a GEC directly to the existing
   grounding electrode, and do not run an EGC to the main service panel.
   - Some combination of the above.


Can anyone point to a clear and concise 3-line diagram that explains the
acceptable options? Hopefully something that and AHJ will consider, like an
IAEI article or NEC Handbook graphic.


Jason Szumlanski
Florida Solar Desing Group
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to