HI Jay,
The Fronius line, primo or symo have that capability. You need the smart meter 
to measure current flow at point of interconnection. The tricky bit is what 
happens when a big load suddenly turns off. There will always be a small flow 
of energy across the meter for a second or two while the system reacts and 
curtails the pv array. HECO was fine with this limited, momentary export of 
energy.These residential systems typically have very low performance factors, 
as the PV peaks around noon, when a typical load profile peaks morning and 
evening. So you end up curtailing most of your pv production. In a commercial 
application though, zero export can work really well, if you size PV to midday 
loads. 
-Wes Kennedy 

    On Wednesday, August 28, 2019, 09:51:40 PM MDT, Jay <jay.pe...@gmail.com> 
wrote:  
 
 Hi Chris, 
So it doesn’t sound like what I’m after. 
I’m looking for a GT WO batteries  hooked to the main panel just like normal 
but having communication from the main ( could be reading smart meter or using 
sensors) to allow power to be consumed in the house but no export to the grid 
by reducing power from the GT inverter. I know it’s done in other countries, 
India for example. 
No sub panel, no dedicated loads panel, no back up, just a normal GT system for 
self consumption with of course the grid suppling what ever the GT inverter 
isn’t. 
Guessing from comments so far I’m SOL. 
Jay
On Aug 28, 2019, at 6:28 PM, Chris Sparadeo <sparadeo.ch...@gmail.com> wrote:


Jay,
My understanding is that the Outback SkyBox is capable of supplying power to AC 
loads (what they call “micro grid”) without needing grid input or a DC storage 
system. Kind of like the SMA SunnyBoy secure power supply, only on a larger 
scale. However, depending on the electrical demands of the loads being 
energized, there is potential that solar PV production would not supply 
necessary power in the daytime...Also, the system would essentially de-energize 
during low irradiance/night times. 
Best,
Chris 
On Wed, Aug 28, 2019 at 9:19 PM Chris Sparadeo <c...@catamountsolar.com> wrote:

Jay,
My understanding is that the Outback SkyBox is capable of supplying power to AC 
loads (what they call “micro grid”) without needing grid input or a DC storage 
system. Kind of like the SMA SunnyBoy secure power supply, only on a large 
scale. However, depending on the electrical demands of the loads being 
energized, there is potential that solar PV production would not supply 
necessary power in the daytime...Also, the system would essentially de-energize 
during low irradiance/night times. 
Best,
Chris 
On Wed, Aug 28, 2019 at 9:03 PM Jay <jay.pe...@gmail.com> wrote:

are there any products out there that can do a grid tie w/o batteries but no 
sell back to the 
grid?

Thx
Jay

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


-- 

Chris Sparadeo

NABCEP Certified PV Installation Professional # 042919-015652


Catamount Solar, LLC

4 Randolph Ave., Randolph, VT 05060

C_(802) 369-4458

O_(802) 728-3600

www.CatamountSolar.com







-- 
Chris Sparadeo

C_802-369-4458H_802-728-3059

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to