I've AC coupled off grid with the Sunny Island, but I haven't tried it with Solar Edge.  Can you adjust the Solar Edge coupling window to outside the IEEE set points?  We used to have set all GT inverters in Hawaii wider, because the utility wanted them to stay on longer in a brown out.

Ray Walters
Remote Solar
303 505-8760

On 7/25/19 5:55 AM, Howie Michaelson wrote:
Hi Ray,
I get the issues with AC coupling.  However, this system already has a 3+ kW DC coupled array, the new array is close to 200' away, and it would take 2 more charge controllers of any of high voltage ones for this size array. Are there any battery based inverters that folks have had decent luck with AC coupling in an off-grid environment?  (My preference would be the XW+).
Thanks,
Howie

On Thu, Jul 25, 2019 at 1:43 AM Ray <r...@solarray.com <mailto:r...@solarray.com>> wrote:

    I do not recommend AC coupling for off grid, except to offset
    daytime loads or to add PV at remote buildings. Besides coupling
    errors like you're experiencing, the entire system will shut down
    and not recharge, if the VFX inverters shut down.   With a DC
    coupled array, the batteries can recharge, even if the inverters
    have shut down for low voltage, over load, etc.  At least when
    someone comes to reset it, the battery won't be dead too. The 3rd
    reason, as you've found, SE and other GT manus, don't want to deal
    with off grid.

    There are higher voltage, higher capacity Charge controllers
    available now, like the FM100, and Magnum PT 100 that could almost
    handle that array with one controller.  The PT 100 will work with
    Midnite's SOB rapid disconnect system.


    Ray Walters
    Remote Solar
    303 505-8760

    On 7/24/19 11:03 PM, Howie Michaelson wrote:
    sorry, prematurely emailed previous post:

    I'm wondering if the VFXs are just not capable of putting out
    clean enough power in order to hold the SE HD inverter. I had it
    operating on this same system for a couple of hours with not this
    problem.  Is it likely that this inverter combo is not going to
    work consistently?  Will it make sense to use a different battery
    inverter (XW+6848 or Radian)? What has folks experience been in
    similar off-grid AC coupled SE systems?
    As always, thanks in advance for any thoughts.

    Best,
    Howie

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to