Hi Mac

I don’t know if this is pertinent, but it could be the SOC /fndc getting out of 
calibration. 

I’ve seen this happen if  % SOC charge termination is on ( default). 
Kinda goes into a negative loop. 

The other thought is that 2 hr absorb is pretty short for that size bank, but 
maybe that is OB spec?

Jay
Peltz power. 

> On Apr 19, 2019, at 10:27 AM, Mac Lewis <maclew...@gmail.com> wrote:
> 
> Hello Wrenches,
> 
> We recently inherited an Outback system that I've been keeping an eye on via 
> Optics.  Its a dual stack 3648 VFXR, with about 4kW of PV with a single 
> string of EnergyCell 1100RE battery bank (reported to be ~6 months old) ~.46 
> kWh at C20.
> 
> I have been observing how the system functions and how the voltage behaves.  
> We keep getting 2 minute voltage starts on the generator in the middle of the 
> night that don't seem necessary judging from how much energy has been used 
> from the battery bank.  I am hesitant to tweak anything because these battery 
> set-points are a bit different than I'm used to.
> 
> As per Outback:
> Absorb Voltage is 55.6V for 2 hours
> Float Voltage is 54.0V
> 
> I've slowly been dropping the 2 minute start voltage to see if there is a 
> bottom, but I'm hesitant to take it much lower (maybe I should). 
> 2 minute start voltage: 44.8 V.
> 
> 
> The system easily charges the battery bank to 100% (and easily reached the 2 
> hr absorb time) every day.  The flexnet DC is correctly set up and calibrated.
> 
> The load on the system is pretty consistent.  They use between 400 and 600W 
> throughout the night.
> 
> An average night, they may use about 6 kWh before the voltage sags below the 
> 2 minute start voltage and it starts the generator.
> 
> Just curious if our 2 minute voltage needs to be dropped or if these 
> batteries are degraded.  What corrective changes can I make to get better 
> performance?
> 
> I have and will call Outback about this, but I'd like other perspectives as 
> well.
> 
> Thanks as always for your expertise
> 
> -- 
> 
> 
> 
> Mac Lewis
> 
> "
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to