Good question.  Voltage slowly drops in a fairly linear fashion through out
the night.  If it is a sudden short duration load, it is short  enough that
Optics can't pick it up, or it get's averaged out.  When I've been on site,
I didn't observe any loads that caused concern.

On Fri, Apr 19, 2019 at 11:45 AM Roy Rakobitsch <winds...@gmail.com> wrote:

> Using Optics, can you equate the voltage sag/ gen start command with a
> particular load?  Or is the voltage dropping quite evenly over the course
> of the night?  They could actually be degraded if there is no indication of
> a sudden load/ voltage drop. A simple load test when on site can also help
> you replicate and/or get a better picture of whats going on.
>
>
> Roy Rakobitsch
> NABCEP Certified Small Wind Installer®
> Certified Advanced Tower Climbing, Safety & Rescue
> Wind/PV Design Engineer
> Windsine LLC
> 631-514-4166
> www.windsine.org
>
>
>
>
>
> On Fri, Apr 19, 2019 at 12:27 PM Mac Lewis <maclew...@gmail.com> wrote:
>
>> Hello Wrenches,
>>
>> We recently inherited an Outback system that I've been keeping an eye on
>> via Optics.  Its a dual stack 3648 VFXR, with about 4kW of PV with a single
>> string of EnergyCell 1100RE battery bank (reported to be ~6 months old)
>> ~.46 kWh at C20.
>>
>> I have been observing how the system functions and how the voltage
>> behaves.  We keep getting 2 minute voltage starts on the generator in the
>> middle of the night that don't seem necessary judging from how much energy
>> has been used from the battery bank.  I am hesitant to tweak anything
>> because these battery set-points are a bit different than I'm used to.
>>
>> As per Outback:
>> Absorb Voltage is 55.6V for 2 hours
>> Float Voltage is 54.0V
>>
>> I've slowly been dropping the 2 minute start voltage to see if there is a
>> bottom, but I'm hesitant to take it much lower (maybe I should).
>> 2 minute start voltage: 44.8 V.
>>
>>
>> The system easily charges the battery bank to 100% (and easily reached
>> the 2 hr absorb time) every day.  The flexnet DC is correctly set up and
>> calibrated.
>>
>> The load on the system is pretty consistent.  They use between 400 and
>> 600W throughout the night.
>>
>> An average night, they may use about 6 kWh before the voltage sags below
>> the 2 minute start voltage and it starts the generator.
>>
>> Just curious if our 2 minute voltage needs to be dropped or if these
>> batteries are degraded.  What corrective changes can I make to get better
>> performance?
>>
>> I have and will call Outback about this, but I'd like other perspectives
>> as well.
>>
>> Thanks as always for your expertise
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> *"Yo solo sé que no sé nada." -Sócrates*
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to