Gary- I am assuming the array is 600v based on string length. Perhaps a few more of the 33kW CORE1s might be a better design fit - could they be mounted off the ground at the combiner locations? Then you utilize 8 of the 12 inputs of each inverter. This would require a couple more conductors go to each inverter location and become AC homeruns to an AC collection panel at Satcon location. The CORE1s cannot run multiple inputs in parallel mode as the A and B channels of the current Sunny Boys can, so I think what you are trying to do will not work. Feel free to contact me directly if you want to discuss further. Best regards- Mike
SMA America Michael Mahon Technical Trainer SMA Solar Academy 916-918-9412 www.SMA-America.com/partners/SMA-Solar-Academy/overview.html ________________________________ From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> on behalf of gary easton <g...@arp-solar.com> Sent: Thursday, April 4, 2019 5:21 PM To: RE-wrenches Subject: [RE-wrenches] De- combining Hello Wrenches We have a project taking a 480kw carport array feeding a Satcon 500kw inverter and upgrading it to 8- 50 kw SMA inverters. The SW 285's, in strings of 12, are combined in groups of 8 in the field then fed to the inverter DC input. In my experience SMA sells a rapid shutdown box with 4 inputs but only 2 outputs to pair with their Inverters that have 3 MPPT channels and they instruct you to combine the strings at the rapid shutdown box on the roof then install a pigtail on that wire at the inverter splitting it into two and sending the output of those two combined strings into two seperate MPPT channels. We would like to do the same with combiner panels in reverse. I spoke with SMA and they are checking with Germany but I knew I would find info here. Anyone with experience with this? -- Gary Easton Appalachian Renewable Power llc. Proud to Celebrate over 10 years in business Stewart, Ohio 45778 NABCEP Certified Solar PV #031508-29 T: 740-277-8498 www.arp-solar.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.arp-solar.com&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Cebca37112fd24de56f2a08d6b95ca14a%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C636900204844313111&sdata=Nfx3kLhzRmC%2BAavBiJzejsgMnBd9KJbFCPev9h4l0fY%3D&reserved=0> [https://docs.google.com/uc?export=download&id=1naWgmhzXyvgE2nh4NH4Y9EBg5r5cUXUM&revid=0B9ql6_CVYv0OaHZQZDVDRUxSelVsZlIxOXNDYnNwejgwT01vPQ] [https://images.youracclaim.com/images/6e7f1abf-3a78-4eb7-bb69-2e687aff5a35/NABCEP_2BBadge_2Blogo_2BPVIP_2B2019_2BFINAL-01.png] “First they ignore you. Then they laugh at you. Then they fight you. Then you win.” ~Gandhi
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org