William –

Not sure what array size you intend to use, but with the Sunny Boy 3.8-US unit 
at 208V the max output power is 3.33kW (as current is limited to 16A for 
breaker sizing at 240V).  So 3 of these units gives “balanced” 3 phase 10kW, 
but at the cost of three inverters.

Two input channels available for each inverter, so you could have an east/west 
oversized array.  Our datasheet specifies the max STC array for the 3.8 is 
5396Wp. (Each input cannot be exposed to more than 18A Isc ever, but each 
channel will draw max 10A in operation.)  Each input channel needs 125VDC to 
start making power, then will work down to 100V (may be lower than CEC 
efficiency though – I would go for higher voltage fewer strings).

And this setup would give the customer three SPS outlets in case of utility 
outage.  Those outlets are 120V each, and cannot be synchronized.  Up to 2000W 
for each, subject to what the array attached to the inverter can produce at any 
given moment.

Best regards –
Mike


SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com<http://www.sma-america.com/>

Solar Academy: 
www.SMA-America.com/partners/sma-solar-academy/overview.html<http://www.sma-america.com/partners/sma-solar-academy/overview.html>

Full training schedule: 
https://www.sma-america.com/partners/sma-solar-academy/seminars/trainings/training/list.html


[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg]<http://www.facebook.com/pages/SMA-America/140290312717395>
 [http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg] 
<http://twitter.com/SMA_America>  
[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg] 
<http://www.smainverted.com/>  [Linkedin Logo] 
<http://www.linkedin.com/company/364675>  
[http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg] 
<http://www.youtube.com/playlist?list=PL840A5336CAC32332>  [SMAAFORUM_ICON] 
<http://smaadvance.com/signup/>
[cid:image008.jpg@01D45E26.3FF7F550]


This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of 
William Miller
Sent: Wednesday, January 16, 2019 7:08 PM
To: Jerry Shafer <jerrysgarag...@gmail.com>; RE-wrenches 
<re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Cost of service upgrade vs Solar credits

Jerry:

Thanks for the reply.  If we go three phase I believe we get to pick our 
voltage.  I understand the options are 120/208, 120/240 (open delta) or 
277/480.  277/480 won’t work for us because of existing equipment operating at 
240 VAC.  We have very few 120 loads so a stinger won’t hurt my feelings—I 
would pick the 120/240.

I can do an AB/AC/BC installation with many residential inverters, but at the 
less than 10K this become problematic:  We actually need to split the 10K 
system size into a 4K and a 6K to offset annual kWh on two meters.  By the time 
you divide these smaller systems into 3 inverters, you don’t have enough panels 
to meet the MPPT lower threshold.  This is where Enphase actually makes some 
sense.  Furthermore,  too many string inverters makes the job expensive.  It 
looks like there are real three phase inverter options and I will keep looking.

I won’t touch a Fronius.  The new equipment may be improved, but I am still 
burnt by a 500% failure rate of IG inverters and some serious character 
assassination by Fronius management in dealing with clients.

I misquoted the $20K cost to upgrade.  This number came from an earlier 
hypothetical scenario.  I need to get real numbers for this project to perform 
an accurate budget analysis.

Thanks for the great input, both online and offline.  I feel like we are 
family.  While the complexities of these projects can be a headache, they make 
the job interesting.

William

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to