Yea, I almost always replace the on board controller on the Anandas.  On some I might keep a small original array on it, but I always have large controller with 3 stage PWM going.

Ray Walters
Remote Solar
303 505-8760

On 10/8/18 8:22 AM, Bradley Bassett wrote:
I have one of the first batch of Ananda with the Heinemann breakers. I've used it with FX inverters and an XW inverter. Mating it up with the FX was difficult, I ended up with an 8x8 gutter between them, and 2" offsets on both sides. Using the conduit box on the XW was easy. I'd expect using the conduit box on the Magnum would be straightforward as well. If I were to try it with an FXR again I'd use an FW250 as a conduit box. But definitely take out the Ananda charge controls and convert to ones that match the new inverter. Unless you're adding more solar that can do a good finish charge then the on/off control for part of the array may be ok.

Brad
AEE Solar

On Sun, Oct 7, 2018 at 6:02 PM Ray <r...@solarray.com <mailto:r...@solarray.com>> wrote:

    Greetings Esteemed Wrenches;

    I have yet another customer whose 20+ yr old Trace SW inverter has
    flown
    off to inverter Nirvana.  I have replaced a few over the years and
    never
    quite solved the quandary of whether to replace the entire power
    board,
    or to retrofit a Magnum/ Outback in place of the SW, and keep the old
    Trace DC enclosure.  In this particular case, he has a pair of SW
    4024s
    on an old Ananda power center. I'm considering taking the system
    to 48 v
    as well, since this will let us use the Magnum 4.4 kW inverters. 
    This
    however will also involve rewiring 20 yr old arrays of 50 and 75 watt
    modules......
    What is the consensus on the best replacement practices on these
    legacy
    systems?  I have several out there with the clock ticking down.  My
    current idea is to just keep the Ananda and use Magnum's extension
    boxes
    to connect up the new MS 4448 inverters.  Its a tough call: I've
    replaced a few single SW installs and reused the Trace DC
    enclosure, and
    cursed working in those tiny boxes.  In other cases, I've put up a
    whole
    new system, but wondered if that was over kill too.  It seems to be a
    case of more field installation hours vs more equipment costs.

    Sure be handy, if someone made an SW replacement kit, there are
    still a
    bunch of them out there.

    As always, thanks for all your comments and ideas,

-- Ray Walters
    Remote Solar
    303 505-8760

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to