The link to review the first draft of the 2020 code is not working.  Do you have just the changes for 690?  I'd really like to submit some comments.

Thanks,

Ray Walters
Remote Solar
303 505-8760

On 8/28/18 7:59 AM, Rebekah Hren wrote:
Hi all,
What you need to do now - to get your voices heard about rapid shutdown requirements-  is to make public comments on the first draft of the 2020 NEC. *_Comments are due AUGUST 30 at midnight!!! _*

Here is the link to a press release <https://www.necanet.org/about-us/news/news-release-archive/news/2018/07/02/nfpa-releases-2020-nec-first-draft-for-public-review> with links to read the draft and input your comments:
https://www.necanet.org/about-us/news/news-release-archive/news/2018/07/02/nfpa-releases-2020-nec-first-draft-for-public-review

The process for changing the NEC is standardized by the NFPA and while it may not be perfect, it's what we've got!

Best,
Rebekah Hren

On Tue, Aug 28, 2018 at 6:50 AM cwarfel <cwar...@entech-engineering.com <mailto:cwar...@entech-engineering.com>> wrote:

    I like your solutions to this. Just sticking to rapid shutdown and
    not the fire code, I think a lot of the problems with 690.12 could
    be reduced if the maximum string voltage was 150 or even 250.  It
    reduces the ampacity on a roof for a given power and I feel that
    is more of a danger than array voltage that the Firefighters are
    highly likely to avoid.

    I still cannot get Outback Power to provide a corrected
    installation manual or a start up procedure on the RSI/ICS
    equipment. Two plus months and all I get are repeated vague or
    incorrect information. One expert at OB said that they really
    didn't deal much with Rapid Shutdown............

    I cannot install any more Outback on roofs at this time.

    I'll see if it is ok to provide a link to an online petition to
    change 690.12.


    Chris



    On 8/27/2018 2:13 PM, Ray wrote:

    HI Chris;

    As with all things bureaucratic,  good intentions can go awry
    when actually implemented.  Years ago, I was one of the wrenches
    pushing for some form of disconnect closer to the power source,
    or the PV array.  I had no idea it would come back to bite us
    small off grid folks so hard, though.  I'm not quite for
    scrapping all of 690.12, but I do think it needs some serious
    work. /In or on the building/ needs to be defined more clearly as
    'on the roof'. Ground mounts need a clearer exemption. The PV
    disconnect needs to be clearly defined and also clearly stated
    that the Rapid disconnect system stops there.  The time limit
    needs to be bumped up to 90 seconds: no one is going to throw the
    switch and be hacking on the roof that fast.  The array voltage
    should be 150 vdc, so that lower voltage off grid systems could
    be exempt, and I really think 690.12 should only apply to larger
    arrays (over 10kW) that have long exposed runs of conduit (over
    10 yards) or that cover more than a certain percentage of the
    total roof area.  If an array covers one face of the garage it
    should be exempt, and if it covers half the total roof, then it
    should have Rapid disconnect, for instance.  We need to be
    sensible, do the fire fighters have a good spot to cut and vent
    the roof without electrical hazards or not?

    Its interesting how article 690 has morphed from being almost
    entirely oriented towards off grid in 99 and 02, to now off grid
    is barely even considered. Just look at the lack of thought when
    they wrote the definitions for /DC to DC Converters/.  The solar
    industry has been ready and willing to be thrown under the bus at
    every turn.  I think its about time we started advocating for our
    own self interests like all the other parties involved.  This
    also means that us off grid folks need to be properly
    represented, and off grid considered with all code changes.  I
    think DC coupled PV should have its own section and be separated
    from AC coupled PV.  The systems are so different that it doesn't
    make sense to throw them into the same section.  The emergence of
    article 706 is a step in the right direction.

    Ray Walters
    Remote Solar
    303 505-8760
    On 8/23/18 5:31 PM, cwar...@entech-engineering.com
    <mailto:cwar...@entech-engineering.com> wrote:

    I think Rapid Shutdown should be scrapped professionally and
    personally.  It was ill conceived and ill written.  Anyone
    willing to join me in a petition to CMP 44 and the like, contact
    me off list.

    To your question directly, you have a ground mounted system and
    you are not subject to 690.12 unless your conductors are "in or
    on building" which i cannot seem to find what that actually
    means. Exempted are buildings that are isolated only for the PV
    system This is a big win for installers as almost everyone
    installs systems like this....... Right.    They used to have a
    dimension to this, but I guess that gave installers too much
    information. This is a stupid Code addition for roof mounted pv
    systems, disguised as protecting Firefighters, but not doing so
    in reality. The NEC looks politically compromised by consultants
    and manufacturers who too advantage of this fear mongering. No
    other country with a pv industry has historically done this. Why
    are installers not up in arms about this?

    This is the NEC reference.

    690.12 Rapid Shutdown of PV Systems on Buildings. PV system
    circuits installed on or in buildings shall include a rapid
    shutdown function to reduce shock hazard for emergency
    responders in accordance with 690.12(A) through (D).

    If your system is ground mounted, you are outside the
    "altruistic" intent of 690.12 of protecting Firefighters. Put a
    initiation device disconnect switch at the array.  Any
    supporters of RS should chime in with the support of 690.12 and
    add clarity and guidance to those of us who actually install
    systems and have to deal with this baloney.  690.12 has caused
    more problems for multimode systems than any tariffs, which are
    bad enough. I don' think the industry needs any more "safe
    design and installation" assistance from the CMPs involved with
    this issue.

    Chris Warfel






    On 2018-08-23 00:31, Ray wrote:

    Greetings fellow wrenches;

    I know we have beat this many times but I once again have not
    been able to resolve the contradictory information in 690 in
    regards to implementing 690.12.  As Rebekah Hren pointed out
    before, the diagrams shown in Figure 690.1(b) show that the /PV
    System DC Circuit/ stops at the /PV Disconnect/.  Note 2 says
    specifically the '/PV Disconnect separates the PV system from
    all other systems/'.  But then in the definitions in 690.2 on
    the next page, the new definition of a /P//V System DC Circuit/
    says that it includes DC to DC converter output circuits. 
    (which are Solar Edge module level controls, but could be
    interpreted as a MPPT battery charge Controller?)

    Then 690.12 which only applies to '/PV System circuits in or on
    buildings/', says we have to control conductors more than 3 ft
    after penetrating the building.

    So in my case, I'm looking at a ground mount, and installing an
    external lockable disconnect on the wall before it goes into
    the building.  This will officially be the PV Disconnect.  In
    my interpretation, I should not need to do any Rapid Shutdown,
    because I've essentially prevented the /PV system/ from ever
    entering the building at all ( based on the 5th diagram and
    Note 2) However, I could see an AHJ claiming I had to do RS all
    the way to the output side of the charge controller.

    If this were true, could I simply apply RS equipment from the
    PV disconnect to the output of the charge controller, or am I
    back to module level shutdown for my ground mounted array, or
    could I build a tiny building that just housed the PV
    Disconnect and take the exemption for '/buildings with the sole
    purpose of housing PV system equipment/'?

    Essentially the definitions in 690.2 are too broad, and are at
    odds with the Figure and Notes of 690.1.  They really didn't
    fix this in the 2017 code for us lowly off gridders. Charge
    controllers are covered by article 706.23___/Charge Control/_,
    and NOT by 690.12 at all. IMHO, the charge controller needs to
    be clearly defined and differentiated from DC to DC converters
    like Solar Edge's module level DC equipment.

    I just want to go back to doing solar designs and
    installations, and quit acting like an attorney parsing every
    word of this confusing code language.

-- Ray Walters
    Remote Solar
    303 505-8760

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>




    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


--
             Christopher Warfel, PE
           ENTECH Engineering, Inc.
    PO Box 871, Block Island, RI 02807
                   (401)466-8978

    EEI logo <http://entech-engineering.com>
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



--
Tel: 336.266.8800
NABCEP Certified Solar PV Installation Professional™ 091209-85
NC Licensed Electrical Contractor


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to