The OutBack GFP breaker is generally on the battery side of the charge
control, the RTB breaker for the ICS+ is installed on the array side of the
charge control. I have not seen, nor been told by OutBack engineers, that
there is a GFP in the ICS+ combiner, but that is where the AFCI is.

Brad
AEE Solar

On Fri, Jul 27, 2018 at 5:17 AM, cwarfel <cwar...@entech-engineering.com>
wrote:

> I learned from Outback yesterday that an important step in using this RS
> initiator is not described in the directions. The prewired GFI needs to
> be removed and the conductors connected to their supplied RTB breaker
> that is supposed to be located in the same slot. The GFI function is in
> the combiner box.
>
> Has anyone found Outback instructions describing this?  The person I
> worked with on the phone yesterday could not find any directions to this
> effect.  Chris
>
>
>
> On 7/25/2018 7:23 PM, Scot Arey wrote:
>
> Yes I had also heard from Outback  that AC Coupling not supported.
>
> Too bad because the AC coupling load center was slick setup and
> integration.
>
> Scot
>
> Get Outlook for Android <https://aka.ms/ghei36>
>
>
>
>
> On Wed, Jul 25, 2018 at 10:29 AM -0600, "Kelly Keilwitz, Whidbey Sun &
> Wind" <ke...@whidbeysunwind.com> wrote:
>
> Larry,
>> I recommend considering retrofitting the SolarEdge “StorEdge” Li-ion
>> battery. It’s a high-voltage battery on the PV side of the inverter. We
>> have a few out there now for a few months without a problem. Really like
>> the design concept of the storage on the PV side, increasing system
>> efficiency.
>>
>> We’ve done quite a few AC-coupled systems, which Outback FX, Outback
>> Radian, and SMA Sunny Island/Sunny Boy. The Outbacks require a cutout
>> relay. We won’t do Radian AC-coupling any more, as the setup,
>> documentation, and support is a royal PITA, and have had failures in the
>> “ROCB” automatic cutout breaker. Even when the ROCB doesn’t fail, it often
>> cuts out when it isn’t supposed to, like at the start/end of a float cycle.
>> My understanding is that Outback doesn’t support AC-coupling any more with
>> the Radian.
>>
>> Kelly Keilwitz, P.E.
>> Principal
>> Whidbey Sun & Wind
>> Renewable Energy Systems
>> NABCEP PV Installation Professional
>> WA Electrical Administrator
>> office: 360.678.7131
>>
>>
>>
>> On Jul 19, 2018, at 07:07, Larry Brown <sunmount...@netstep.net> wrote:
>>
>> Does anyone have a recommendation on a battery based inverter to AC
>> Couple with a Solar Edge 11400A-US Inverter that is already installed?
>> I have been working a lot with the Schneider Conergy XW+ Inverters for
>> off grid but have no experience AC Coupling them with a Solar Edge Inverter
>> Any recommendations?
>>
>> Thanks
>> Larry
>>
>> Larry Brown
>> Sun Mountain
>> 845-657-8096
>> sunmount...@netstep.net
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
>
> --
>
>          Christopher Warfel, PE
>        ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
>                (401)466-8978
>
> [image: EEI logo] <http://entech-engineering.com>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to