Hey Nik,

 

Consider these points with your client:

1.      Your racking system most likely has gaps between rows of modules, so 
most/all of the rain that hits modules higher up on the roof will fall through 
that gap and will run on the roof as normal. Only the lowest row of modules 
will collect rain that could “jump the gap”. The 100yr worst rainfall rate in 
Vermont (listed as in Bratteboro) is 2.7”/hr. The quick math has that as 31 
gallons/hr for a standard 60cell module. Which is 0.5gpm. So if they wanted to 
test this, they should be able to let a garden hose lose on a single solar 
module (usually far, far more than 0.5gpm, a short piece of garden hose can put 
out more than 15GPM actually, 30 times the 100yr rainfall rate) and see if that 
is enough water to jump the gap (be sure to face the hose uphill so the water 
has a chance to spread laterally and also not be forced off the module edge at 
an artificially high speed from the water pressure). My bet is that it will 
not. And you most likely just tested at 3-5times the 100yr storm level of 
rainfall in your area.
2.      If the client is not satisfied with the above. Depending on your 
racking system, some racks offer skirts. The skirts usually have a curve down 
to the roof from the module edge, the curve would direct the water down to the 
roof from the bottom row of modules via surface tension. The water layer will 
stick to the skirt and follow it down, even if inertia would normally force the 
water to arc over the gutter. You see that phenomena at water parks sometimes 
where the water slide has a little hump to give the tube riders a bit of air 
time, but the water stays stuck as a film to the water slide itself. Surface 
tension at work.

 

Not to add to your worries, but in Vermont, I’d be more worried of ice sheeting 
on the bottom row of modules and bypassing the gutter, to fall of pedestrians 
or people entering the house if your gutters overhung the entrance. But you get 
a lot of snow in Vermont, so houses there may designed that particular hazard 
out of most home construction.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

 

 

From: RE-wrenches <re-wrenches-boun...@lists.re-wrenches.org> On Behalf Of Nik 
Ponzio, Building Energy
Sent: Monday, April 30, 2018 8:32 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] rain guard

 

We have a roofmount PV array that is very close to the run gutter. The customer 
is concerned that the runoff during heavy rain will overshoot the gutter. So 
I'm looking for a product that will mount at the lower edge of the array and 
slow down the rain water. I looked that Alpine SnowGuards but they all have a 
small gap between top of solar module and bottom of the snow rail. 

 

Any suggestions?

 




--
Nik Ponzio
Building Energy
1570 South Brownell Road
Williston, VT 05495
802-859-3384 ext.115
http://www.BuildingEnergyVT.com

 

 

 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to