It always depends on who you are working with !  Because of you folks
putting solar panels on roofs, I have had a few fire Captains ask about
clearances on ground mounted trackers:(

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

> Darryl:
>
>
>
> If you are talking about California, I must respectfully disagree.  If you
> are not talking about California, I am ignorant.
>
>
>
> California Fire Code, 2016 version, states the following for group R-3
> buildings (which I am fairly certain includes single family homes).  This
> includes provisions for pitched roofs.  Upon first reading, I do not see
> any improvements over the previous version (2012) except that it appears
> clearance from valleys has reduced from 36” to 18”.
>
>
>
> These regulations are implemented by local fire Marshalls in California
> (sometimes the same person as the Chief, sometimes not).  This gives the
> Marshalls complete discretion.  I have had good luck negotiating with
> Marshalls and finding good compromises.
>
>
>
> Excerpt from 2016 California fire code.
>
>
>
> *605.11.1.1 Roof access points. Roof access points*
>
> *shall be located in areas that do not require the placement*
>
> *of ground ladders over openings such as windows*
>
> *or doors, and located at strong points of building construction*
>
> *in locations where the access point does not*
>
> *conflict with overhead obstructions such as tree limbs,*
>
> *wires or signs.*
>
>
>
> *605.11.1.2 Solar photovoltaic systems for Group R-3*
>
> *buildings. Solar photovoltaic systems for Group R-3*
>
> *buildings shall comply with Sections 605.11.1.2.1*
>
> *through 605.11.1.2.5.*
>
> *Exception: These requirements shall not apply to*
>
> *structures designed and constructed in accordance*
>
> *with the California Residential Code.*
>
> *605.11.1.2.1 Size of solar photovoltaic array. Each*
>
> *photovoltaic array shall be limited to 150 feet (45*
>
> *720 mm) by 150 feet (45 720 mm). Multiple arrays*
>
> *shall be separated by a 3-foot-wide (914 mm) clear*
>
> *access pathway.*
>
> *605.11.1.2.2 Hip roof layouts. Panels and modules*
>
> *installed on Group R-3 buildings with hip roof layouts*
>
> *shall be located in a manner that provides a 3-*
>
> *foot-wide (914 mm) clear access pathway from the*
>
> *eave to the ridge on each roof slope where panels*
>
> *and modules are located. The access pathway shall*
>
> *be at a location on the building capable of supporting*
>
> *the fire fighters accessing the roof.*
>
> *Exception: These requirements shall not apply to*
>
> *roofs with slopes of two units vertical in 12 units*
>
> *horizontal (2:12) or less.*
>
> *605.11.1.2.3 Single-ridge roofs. Panels and modules*
>
> *installed on Group R-3 buildings with a single*
>
> *ridge shall be located in a manner that provides two,*
>
> *3-foot-wide (914 mm) access pathways from the*
>
> *eave to the ridge on each roof slope where panels*
>
> *and modules are located.*
>
> *Exception: This requirement shall not apply to*
>
> *roofs with slopes of two units vertical in 12 units*
>
> *horizontal (2:12) or less.*
>
> *605.11.1.2.4 Roofs with hips and valleys. Panels*
>
> *and modules installed on Group R-3 buildings with*
>
> *roof hips and valleys shall not be located closer than*
>
> *18 inches (457 mm) to a hip or a valley where panels/*
>
> *modules are to be placed on both sides of a hip or*
>
> *valley. Where panels are to be located on only one*
>
> *side of a hip or valley that is of equal length, the*
>
> *panels shall be permitted to be placed directly adjacent*
>
> *to the hip or valley.*
>
> *Exception: These requirements shall not apply to*
>
> *roofs with slopes of two units vertical in 12 units*
>
> *horizontal (2:12) or less.*
>
> *605.11.1.2.5 Allowance for smoke ventilation*
>
> *operations. Panels and modules installed on Group*
>
> *R-3 buildings shall be located not less than 3 feet*
>
> *(914 mm) from the ridge** in order to allow for fire*
>
> *department smoke ventilation operations.*
>
> *Exception: Panels and modules shall be permitted*
>
> *to be located up to the roof ridge where an*
>
> *alternative ventilation method approved by the*
>
> *fire chief has been provided or where the fire*
>
> *chief has determined vertical ventilation techniques*
>
> *will not be employed.*
>
> *605.11.1.2.6 Locations of DC conductors. Conduit,*
>
> *wiring systems, and raceways for photovoltaic circuits*
>
> *shall be located as close as possible to the*
>
> *ridge or hip or valley and from the hip or valley as*
>
> *directly as possible to an outside wall to reduce trip*
>
> *hazards and maximize ventilation opportunities.*
>
> *Conduit runs between sub arrays and to DC combiner*
>
> *boxes shall be installed in a manner that minimizes*
>
> *the total amount of conduit on the roof by*
>
> *taking the shortest path from the array to the DC*
>
> *combiner box. The DC combiner boxes shall be*
>
> *located such that conduit runs are minimized in the*
>
> *pathways between arrays. DC wiring shall be*
>
> *installed in metallic conduit or raceways when*
>
> *located within enclosed spaces in a building. Conduit*
>
> *shall run along the bottom of load bearing*
>
> *members.*
>
>
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Darryl Thayer
> *Sent:* Tuesday, April 03, 2018 8:51 PM
> *To:* newrewrenches
> *Subject:* Re: [RE-wrenches] Clearance clarification please
>
>
>
> It is in the building code.  It is for commercial flat roofs not for
> residential
>
>
>
> On Tue, Apr 3, 2018, 2:52 PM <ch...@oasismontana.com> wrote:
>
> Hey folks:
>
>
>
> What section of the Code relates to the 3' clearance for a solar array?
> …as in, the roof area around the array.   I’ve been scrutinizing the
> NEC til
> my eyes are crossed…..
>
>
>
> THANKS!
>
>
>
>
>
> Chris Daum
>
> Oasis Montana Inc.
>
> 406-777-4309
>
> 406-777-4309 fax
>
> www.oasismontana.com
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to