Thank you for the input.  I’m going to purchase a 48V Charger and charger each 
module and monitor it closely.   

 

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Darryl Thayer
Sent: Saturday, February 10, 2018 4:03 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Older iCel System Lithium Ion Batteries

 

Is there not a concern that if the batteries are showing such low voltage that 
they will not accept current, and the voltage will rise to module voltage and 
put array voltage on the output of the charge controller?

 

On Sat, Feb 10, 2018 at 12:24 PM, Ray <[email protected] 
<mailto:[email protected]> > wrote:

Allan has a good approach as long as you are there to monitor it.  The wiring 
is already there, you just have jump the array positive to the controller 
output.  ( a little double lugging never hurt anyone....?!!.)  

Even higher voltage arrays with MPPT can be used this way.  They will just put 
out close to their short circuit current, as the batteries will pull the array 
voltage way down on the IV curve. 

Ray Walters

Remote Solar

 

On 2/10/18 1:37 AM, Sindelar Solar wrote:

Gary, you might try an old-fashioned approach: bypass the controller to send 
the array straight to the batteries until threshold voltage is reached. More 
specifically, bypass one of the controllers; assuming 48, 60 or 72 Vnom 
depending on array. Let the other controller remain in normal operation. Send 
the unregulated array to bring initial battery voltage up; then the other 
controller takes over and the one that was bypassed now is reconnected. Better 
if the unregulated array is the smaller of the two, I would suspect.

What I'm suggesting will work with flooded lead-acid, and likely VRLA lead-acid 
as well, as long as the unregulated array is taken out of the system before 
voltage exceeds bulk. It may not work at all with these Li-I, as I have no 
experience with restoring them. Daryl may well be right about being 
unrestorable below a threshold voltage; also the batteries may need an 
operational BMS to take a charge. So this is perhaps just food for thought.

Allan

-- 

Allan Sindelar
[email protected] <mailto:[email protected]> 
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 <tel:(505)%20780-2738>  cell

On 2/9/2018 6:16 PM, Gary Rochlin wrote:

Does anyone have any information or specifications for an older circa 2010-2012 
iCel System Lithium Ion Battery.  We are doing a repair on an older 48V Lithium 
Ion system consisting of 3-6 ICel batteries wired in parallel and 1 Xantrex 
6848 and 2 Xantrex Conext MPPT 60 150 Solar Charge controllers.  Via a surge 
from SCE system shut down and sat before we were called in.  Batteries are 
sitting at 6.67V and the charge controller will not turn on unless the 
batteries are at 40V since at the time they were made for lead acid batteries.  
I’m looking at finding the way to charge the iCel  batteries or goose the 
charge controller into thinking 40V are coming from the batteries.  I think I’m 
making sense here.  

Blue Sky Energy 

 <mailto:[email protected]> [email protected] 
<http://blue-sky-energy.com> 

_______________________________________________
List sponsored by Redwood Alliance
 
List Address: [email protected] 
<mailto:[email protected]> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

 

 

_______________________________________________
List sponsored by Redwood Alliance
 
List Address: [email protected] 
<mailto:[email protected]> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 
 

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to