Wayne
We will not connect a grid tie inverter down stream of a gen-set, you don't
want the inverter attempting to connect, when it comes right down to it,
Why would you want to it would be a very small micro grid that if and when
the demand is less then the inverter output would be then the gen-set would
produce no power, volts yes amps no, then the volts climb the inverter
discos and bam the genny has to make it all up. We have 8 k to 250 k gennys
and PV systems attached all are upstream or in switches to turn them off.
Jerry

On Thu, Jan 11, 2018 at 3:54 PM, Wayne Irwin <pureenergyso...@hotmail.com>
wrote:

> Hello All,
>
>
> We have several customers adding generators to their homes on which we
> have previously installed PV systems.
>
> Historically most generators didn't produce a clean enough 60Hz sinewave
> to get the inverters to feed back.
>
> However, with the generator technology improving and the introduction of
> inverter generators, I'm concerned that if the inverters feed back to the
> generator it will smoke the stator.
>
>
> I'm wondering if any of you have any experience/issues?  If so, what
> solutions or recommendations do you have?
>
>
> Thanks,
>
>
>
> Wayne Irwin,
> President
> License #CVC56695
> State Licensed Solar Contractor
> Pure Energy Solar International Inc.
> wa...@pureenergysolar.com <pureenergyso...@hotmail.com>
> <http://pureenergysolar.net/>http://PureEnergySolar.com
> http://SolarChargingStation.net <https://solarchargingstation.net>
> 352 377-6527 <(352)%20377-6527> Office
> 352 336-3299 <(352)%20336-3299> Fax
>
>
> The Sun Is Always Shining!
>
> The content of this message is Pure Energy Solar Confidential. If you are
> not the intended recipient and have received this message in error, any use
> or distribution is prohibited. Please notify me immediately by reply e-mail
> and delete this message from your computer system. Thank you.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to