August

  We had something similar happen a few years ago on an AC coupled application 
using a 5048 Sunny Island ( with transformer ) and a Sunny Boy 7000. In a grid 
down scenario the Sunny boy dropped off line.  After a few calls with SMA 
sharing the error codes it turned out the Sunny Island was not delivering 60 
hertz, not even 59, so we had to reprogram the Sunny Boy to recognize and run 
on 57 hertz.

  SMA was gracious enough to share the "magic code " and walk me through the 
programming. Once the Sunny Boy was reset to operate on the lower hertz range 
everything worked great. You may have a similar situation, not sure if the ABB 
folks will help with the hertz adjustment but you should give it a try before 
springing for a sunny boy.

Peter Giroux
ASAE
  ----- Original Message ----- 
  From: August Goers 
  To: RE-wrenches 
  Sent: Monday, September 18, 2017 5:48 PM
  Subject: [RE-wrenches] Sunny Island grid tie battery back and backup 
stability issues with ABB


  Hi Wrenches -


  We have an ~3 year old grid tied battery backup system with a SMA Sunny 
Island 4548 and Power-One (now ABB) PVI-5000 inverter. There is also an Outback 
PSX-240 to boost the Sunny Island voltage to 240 volts. 


  We recently returned to the site for an annual service call and tested the 
system by simulating a power outage. The Sunny Island kicked in just fine and 
provided stable voltage for the backup loads. However, the ABB tries to connect 
and immediately we see that voltage and frequency of the Sunny Island grid 
start to rapidly fluctuate. I have a feeling that my Fluke meter is not 
capturing the fluctuations properly, but I was seeing voltage fluctuate in the 
238 to 242 volt range and frequency rapidly fluctuate between 59 and 61 Hz. 


  The ABB connects for a minute or two and then gives us a grid out of range 
error. This occurs when we have lots of irradiance and also under relatively 
low light conditions. I've already been on the phone with SMA tech support 
several times and verified that all the Sunny Island settings are good.


  Has anyone else seen this type of instability issue and did you find a fix? 
We might need to install a Sunny Boy. 





  Thanks,


  August

  August Goers

  Luminalt










------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: RE-wrenches@lists.re-wrenches.org

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to