Wrenches We are getting some questions from PRMD some questions relating to 690.8 here is what we have 3 modules, 260 watts at 9 amps ISC each module is a single string which goes into a MNPV6 disco/combiner/disconnect combined to a 30 amp breaker, it is being replaced with a 40 amp per 690.8(A) 1 leaves there and goes to a 32 amp disconnect in our device. here is where it gets interesting 690.8 (A) requires the 40 amp breaker but reading down to 690.8 (B) 1 we need to up-size to 50 amps (no 45 amp is non available) We also have added the 63 amp GFI in the disco we have also moved up from # 10 wire to # 8 wire as a result All this seams over kill for three modules, there are 2 exceptions but PRMD do not feel they are relative. Is the Midnite solar disco considered an assembly with the bus bars inside if we install the breakers Any ideas would be helpful Jerry
_______________________________________________ List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org