Eric,

Your reasoning sounds logical, but it is missing the point. Transformers have 
to be protected by overcurrent devices, similar to wire. Inverters are current 
limited devices so they only have to be able to withstand a certain size 
circuit breaker. The current from the inverter is considered continuous so most 
circuit breakers are designed to operate at 80% of their rating continuously 
(therefore the requirement to multiply inverter output current by 125%).

 

Does that make any more sense?

 

Bill.

 

Bill Brooks, PE

Principal

Brooks Engineering

3949 Joslin Lane

Vacaville, CA 95688

707-332-0761 (office and mobile)

b...@brooksolar.com (email)

www.brooksolar.com (web)

 

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of e...@harvesthesun.com
Sent: Monday, October 31, 2016 3:34 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] Undercurrent Protection?

 

I realize this is potentially a stupid question, and one that is long overdue, 
but here goes:

 

Why in 690(B) are we setting a minimum threshold on OCPD when we're protecting 
against over current?

 

Shouldn't we be setting a maximum threshold...as is done in pretty much all 
other cases? The way I see it, we should take the array/inverter max output AC 
current and multiply by 125% to set our min ampacity on wire,

and then calc down to find the breaker trade size that lands between the max AC 
output current and max AC output current times 125%. That way, we avoid 
nuisance tripping but achieve the max overcurrent protection possible.

By following 690(B) we're actually decreasing OCP: Literally, 690(B) is stating 
that we can have a breaker 100x over the circuit rating, so long as it's not 
under the circuit rating times 1.25. To me this seems antilogical.

 

Mr. Brooks?

 

690.9(B) Overcurrent Device Ratings. Overcurrent device ratings

shall be not less than 125 percent of the maximum

currents calculated in 690.8(A).

 

455.7(B)...The overcurrent protection determined

from this section shall not exceed 125 percent of the

phase converter nameplate single-phase input amperes.

 

450.4(A)...Such overcurrent device

shall be rated or set at not more than 125 percent of

the rated full-load input current of the autotransformer.

 

450.5(A)(2) Overcurrent Protection. An overcurrent sensing device

shall be provided that will cause the main switch or commontrip

overcurrent protection referred to in 450.5(A)(1) to open if

the load on the autotransformer reaches or exceeds 125 percent

of its continuous current per-phase or neutral rating.

 

450.5(B)(2)(b) Ampere Rating. The overcurrent protection shall be

rated or set at a current not exceeding 125 percent of the 

autotransformer continuous per-phase current rating or

42 percent of the continuous-current rating of any seriesconnected

devices in the autotransformer neutral connection.

 

 

 

Eric Stikes

Founding Director & CEO

Good Sun Solar, A CA non-profit corp.

www.goodsun.life <http://www.goodsun.life> 

(530) 559-5023

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to