Not sure about the rest but under ground conductors are considered a wet 
location. 

Jesse Dahl

NABCEP PV Installation Professional
IBEW Local 292 - Electrician 
Electrical/Solar PV Instructor - HCC

Sent from my iPhone

> On Jun 23, 2016, at 3:41 PM, Peter Parrish <peter.parr...@calsolareng.com> 
> wrote:
> 
> I am working with a customer who is doing a complete remodel, and upgrading 
> to PV and Smart Energy Storage. The house was broken down to floor joists, 
> open studded walls and open roof rafters.
>  
> The client wanted a 8 kW/16 kWh Smart Energy Storage system and a 10 kW-ac PV 
> system. The Main panel, the Critical Load sub-panel, the Energy Storage 
> system and the PV inverters will all be either in a detached garage or hung 
> on the west facing exterior wall of the detached garage.
>  
> We have been given a number of 1-1/2” PVC conduits, buried a minimum of 18”,  
> that run between the main house and the detached garage, so we have to convey 
> 2/3rds of the PV source circuits and all of the critical load branch circuits 
> using this conduit. This raises a number of questions/confirmations:
>  
> (1)    We cannot mix PV source circuits and critical load branch circuits in 
> the same conduit. Pretty obvious.
> 
> (2)    What ambient temperature should I use in my ampacity calculations? I 
> assumed something less than 30°C, such as 20°C. But I read somewhere that one 
> has to be careful when the conduit exists the ground, in that one has only 
> 18” of conduit above ground before one has to use the full maximum ambient 
> temperature which in our case is 45°. The argument says that for the first 
> 18”, the portion of the copper conductors in the ground will cool the portion 
> of the conductors above ground via thermal conduction. I can’t find any 
> citation to confirm this argument. Does anyone have any sources of 
> information on the subject? Even if there is a sound engineering basis for 
> the argument, soon after exiting the ground, one would need a vault to splice 
> in a higher ampacity conductors and continue on to either the critical load 
> sub-panel or the inverters, you have to calculate the ampacity at 45°C. These 
> buried conduit runs are approximately 50 feet in length.
> 
> (3)    One end of the conduit run is supposed to come out of the ground 
> inside the building envelope, so we could derate using 30°C or so for air 
> conditioned space. We cannot count on the garage being air conditioned 
> however.
> 
> (4)    Can we use THHN as opposed to THWN-2? I am assuming the forces of 
> nature or human stupidity will eventually cause the PVC to crack and the 
> extra expense of THWN-2 (or another wet rated 90°C  conductor) will be a 
> better choice.
>  
> This job is the same one where the electrician claimed that neutrals on a 
> 120V branch circuit don’t count as current carry conductors in conduit for 
> the purposes of de-rating ampacity. He’s gone, but his replacement may not be 
> any more careful in his ampacity calculations.
>  
> Faithfully yours,
>  
> Peter T. Parrish, Ph.D.
> NABCEP™ Solar Professional #031806-26
> President, SolarGnosis
> 1107 Fair Oaks Ave.
> Suite 351
> South Pasadena, CA 91030
> (323) 839-6108
> peter...@pobox.com
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to