Chris,

 

While John’s article may seem like a logical interpretation of the 2014 NEC, if 
you lived in the western half of the United States where these panels are 
common, you would have a very different view of his choice of articles.

 

His article sites a technicality that is not a safety concern in the least. Of 
all the things that AHJs have to worry about with PV, this has to be at the 
very bottom of the list—and yet this is the only thing that many AHJs look at 
because someone wrote an article about it. We set the record straight in the 
2017 NEC, but that does not fix the fact that literally 1,000s of these 
perfectly fine panels have been removed due to the focus of this magazine 
article.

 

Your opinion of this interpretation would be very different if you had lost a 
PV system sale because someone was unwilling to incur the extra cost of a panel 
change out when you knew it was totally unnecessary.

 

I have all the respect in the world for what you are doing in the northeast. 
I’m just helping with some “perspective” from the left coast.

 

I’m off my high horse,

 

Bill.

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Christopher Warfel
Sent: Thursday, March 03, 2016 6:42 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

 

This is a link to John Wiles article on NEC2014 for this topic. To my 
knowledge, no one has adopted NEC2017, so it would seem that this article is 
appropriate for the most recent NEC published. As noted AHJs can allow 
exceptions, and it is great that new language is now approved for NEC2017, but 
that wasn't the case when John Wiles published his article.

http://iaeimagazine.org/magazine/2014/07/10/center-fed-load-centers-and-panelboards/

There is also pdf version here.

https://www.google.com/url?sa=t 
<https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&ved=0ahUKEwjl8OmH26TLAhWI7D4KHcbJAHQQFggjMAE&url=http%3A%2F%2Fdept-wp.nmsu.edu%2Fswtdi%2Ffiles%2F2015%2F11%2Fiaei_jul-aug_2014.pdf&usg=AFQjCNERV2M21V1nvLlvLVSLZUMoj36J_A&sig2=g145SdF1HzNuHc0P6NXshw&bvm=bv.115339255,d.cWw&cad=rja>
 
&rct=j&q=&esrc=s&source=web&cd=2&ved=0ahUKEwjl8OmH26TLAhWI7D4KHcbJAHQQFggjMAE&url=http%3A%2F%2Fdept-wp.nmsu.edu%2Fswtdi%2Ffiles%2F2015%2F11%2Fiaei_jul-aug_2014.pdf&usg=AFQjCNERV2M21V1nvLlvLVSLZUMoj36J_A&sig2=g145SdF1HzNuHc0P6NXshw&bvm=bv.115339255,d.cWw&cad=rja


Chris




On 3/2/2016 2:24 PM, billbroo...@sbcglobal.net 
<mailto:billbroo...@sbcglobal.net>  wrote:

All,

 

Here is the new language that has been approved for the 2017 NEC (more 
authoritative than JW).

 

705.12(B)(3)(d)

 

(d) A connection at either end, but not both ends, of a center-fed panelboard 
in dwellings shall be permitted where the sum of 125 percent of the power 
source(s) output circuit current and the rating of the overcurrent device 
protecting the busbar does not exceed 120 percent of the current rating of the 
busbar.

 

This clarifies that it was never the intent of the NEC to limit the 120% rule 
to the opposite end of the busbar for dwellings (it was allowed from 2005 back 
to 1987). I was able to convince the panel that centerfed panels did not need 
the opposite end stipulation. Several large jurisdictions in California or 
considering making an official policy accepting the language of the 2017 NEC on 
this item. Please share this with your own jurisdiction.

 

Bill.

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Glenn Burt
Sent: Wednesday, March 02, 2016 10:54 AM
To: RE-wrenches  <mailto:re-wrenches@lists.re-wrenches.org> 
<re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

 

I believe that John Wiles has stated this in a couple of places in print, 
therefore you may have a tough time justifying a way around the rule to an AHJ.

Supply side connections are very popular in this situation.


  _____  


From: August Goers <mailto:aug...@luminalt.com> 
Sent: ‎3/‎2/‎2016 11:32
To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org> 
Subject: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for 
center-fed panelboards

All –

 

We are seeing more AHJs not allowing us to use the NEC 7015.12(D)(2)(3)(b) 120% 
rule on center-fed panelboards. For example, if we have a 100 A meter/main 
combo with a center fed 100 A breaker we cannot apply the 120% rule at all and 
need to do a panel swap. What are other wrenches doing in this case?

 

Best,

 

August

Luminalt






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org> 
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 
 
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 
 





-- 
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to