Hi jerry

Can you give any insight as to the failure mechanism?  

I guess I don't understand why bad AC would damage the inverter, I mean besides 
the obvious bad equipment design. 

Jay
Peltz power. 

> On Jan 29, 2016, at 3:18 PM, Jerry Shafer <jerrysgarag...@gmail.com> wrote:
> 
> We have seen something very close, it appears that the gwnny will always win 
> this war.
> Jerry
> 
>> On Jan 29, 2016 1:14 PM, "Jason Szumlanski" 
>> <ja...@floridasolardesigngroup.com> wrote:
>> I'm looking at two Eaton PV250 inverters that failed simultaneously as far 
>> as we know (not my install). Everything checked out normal, but no display 
>> and no power output. I suspect both boards are bad. Upon digging into the 
>> scenario I discovered that the owner had a whole-house generator transfer 
>> switch installed a while back, after the PV was installed. The PV is a load 
>> side interconnection, so calamity should have been expected.
>> 
>> What are the odds that the generator caused the inverter boards to fail? I 
>> was always under the impression that it was more likely for a generator 
>> component to be damaged than an inverter component in this scenario. It 
>> could be coincidence and the inverters may have just failed around the same.
>> 
>> Note:  ~10kW PV, 25kW Generator
>> 
>> Side note: The PV was interconnected at a 50A breaker on a 200A bus bar in 
>> the main distribution panel and somehow passed inspection by an AHJ that 
>> shall not be named... Over 120%, and also not the correct OCPD rating anyway 
>> for these two inverters. Passed plan review and inspection... Contractor out 
>> of business... surprise!
>> 
>> 
>> Jason Szumlanski
>> Florida Solar Design Group
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to