Allan, No, not suggesting to get rid of E-panels or wiring centers. They aren't optimum though, electrically speaking. My suggestion was more of a technical one intended to illustrate a way of wiring to reduce stress on (most) MPPT charge controllers. I should not have said it was a a good practice "these days"... That was kind of dumb for me to say.

With the battery electrically a few feet away from the battery buses, that tie the inverter and charge controllers together (plus other components), the CCs and other energy sources
can be momentarily short-circuited by the inverter (various reasons)...

If that bus was right at the battery terminals, then it's not nearly as much stress on things. This is because the battery keeps a low impedance voltage point between the two different systems.... This assumes that the batteries are in decent health.

You probably won't notice any issues wiring just the way you have been doing things all these years so I would just keep doing what you are doing. With proper over current
protection (OCP), stress and reliability won't be an problem.

But, it doesn't hurt to keep this concept in the back of your mind when thinking about
how things work.

boB


On 10/31/2015 6:12 PM, Allan Sindelar wrote:
boB,
I appreciate your contribution to this discussion, but it brings up a couple of issues for me.

- You have suggested that "A good wiring practice these days is to...wire the controller's battery terminals close or right at the battery terminals." This goes against all modern good practices of which I'm aware. We have long accepted as standard a single pair of battery cables, with all DC input and distribution handled within the power center (I've heard that some people refer to these things as 'E-Panels'). It's the only way to effectively run all current through a shunt on the negative, and through proper overcurrent protection/disconnects on the positive.

I must not have understood what you meant, as it sounds like you're suggesting abandoning the entire E-Panel approach. What am I missing here?
Thanks, Allan

*Allan Sindelar*
al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

**

On 10/29/2015 7:10 PM, b...@midnitesolar.com wrote:
On 10/29/2015 5:02 PM, Jay wrote:
boB,
Is the OCP still being used and does it work in both directions?
JAY, Peltz power

Hi Jay. Yes, the OCP you refer to is still there. This particular OCP though is a hardware fast OCP intended to protect the controller against large load surges on the battery side of the controller... This usually happens when battery cables are long and the inverter(s) are connected electrically close to the controller, thereby drawing huge amounts of current from the Classic than from the battery when the inverter is turned on, charging its input capacitors or something with huge AC loads.

A good wiring practice these days is to, if convenient at least, wire the controller's battery terminals close or right at the battery terminals. Then, when an inverter is either turned on and giving a momentary short circuit to the battery lines, that current will come from the battery rather than the controller's electronics.

Larger cables won't necessarily fix the problem due to battery cable inductance.

The 150s and 200s rarely need the OCP circuitry. The 250 is the one the OCP was
really designed for but we put it into all of the controllers.

There is also over current protection going the other way but is not a microsecond timed protection. Plain old fast or slow ramping up surges like we're talking about is easy to
control, normally.

Breaker tripping like this is extremely rare, IF it is from this kind of current spikes due to generator startup. I would suggest to be safe and bring another controller up just in case.

Might be a bad controller but I just don't know without logging or observing it happening with a scope and a current probe. I've seen some very strange things happen.

boB
Sent from my iPhone
On Oct 29, 2015, at 4:19 PM, "b...@midnitesolar.com" <b...@midnitesolar.com> wrote:

Larry, because these MPPT CC's are bi-directional (for efficiencies' sake), they can convert a large current at the battery side to a smaller current at the PV side if not adjusted right. Normally this is just taken care of and reduced to a bare minimum by the controller watching the voltages and currents carefully. It is technically possible though for things to not work exactly correctly. I am not saying that this is for sure happening, but it is possible. The ramping up in battery voltage from the chargers should be plenty slow enough for this not to be a problem but I am wildly speculating that this could happen and cannot rule it out. There may of course be something else completely different happening here
though.

If CBI breakers are being used, these are known to be extremely fast at tripping when overloaded.

Also, what, if any SPDs are connected to the system ?

boB


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to