This one is easy to misinterpret. You missed the words “live parts”. This has 
been removed from the 2017 NEC because it is actually referring to load 
circuits being fed directly by a PV system on the dc side. All references to 
loads and batteries are being removed from 690.



This is a complete non-issue.



Bill.



From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Craig Gerald Buttke
Sent: Thursday, September 03, 2015 11:44 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Guarding against live parts 690.7 (D)





How is everyone handling 690.7 (D)

Circuits over 150 Volts to Ground. In one- and two- family dwellings, live 
parts in photovoltaic source circuits and photovoltaic output circuits over 150 
volts to ground shall not be accessible to other than qualified persons while 
energized.



If you have a commercial (non one or two-family dwelling) are you screening 
your ground mount arrays to keep people from touching live conductors PV wires)?

Thanks for your thoughts



--
Yours in Solardarity,

Craig Gerald Buttke

M:(715) 630-1227
O:(715) 630-6451
F:(715) 952-4501

North Wind Renewable Energy, LLC
1626C W Pearl Street
Stevens Point, WI 54481

www.northwindre.com <http://www.northwindre.com>

NABCEP Certified PV Installation Professional™
NABCEP Certified PV Technical Sales Professional™
State of WI: Master Electrician


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to