We sent a response this morning, this would have been a good addition to show 
precedent. If they turn us down after this, we will likely take them to appeals 
court. We just can’t let our state code agency try to enforce a rule that is 
clearly wrong, and hurts the potential for future projects so drastically.

 

This is what we sent this morning:

 

 

We fully believe by definition that the 10’-0” clearance requirement as stated 
on Correction Letter #1 dated 08/13/15 does not include Solar PV modules. 
Please review the attached Code references for further explanation.

 

OBC 2011

1013.5 Mechanical equipment. Guards shall be provided where appliances, 
equipment, fans, roof hatch openings or other components that require service 
are located within 10 feet (3048 mm) of a roof edge or open side of a walking 
surface and such edge or open side is located more than 30 inches (762 mm) 
above the floor, roof or grade below. The guard shall be constructed so as to 
prevent the passage of a sphere 21 inches (533 mm) in diameter. The guard shall 
extend not less than 30 inches (762 mm) beyond each end of such appliance, 
equipment, fan or component.

 

This section of code is intended for Mechanical equipment, equipment with fans, 
controllers, refrigerant, ducts, etc… that do require service during their 
designed life. 

 

Solar PV modules are not mechanical equipment, they are solid state electrical 
components that require no service during their design life, they in-fact 
contain no serviceable parts whatsoever. As such the Solar PV modules are also 
not subject to the working space requirements of NEC section 110 (specifically 
110.26 (A) which further stipulates that working space is needed around 
equipment “…operating at 600 volts, nominal,  or less to ground and likely to 
require examination, adjustment, servicing, or maintenance…” ).

 

IB 2015

The 2015 IBC 1512.1 states that Photovoltaic Modules shall also be installed 
with compliance to the IFC. The 2015 IFC 605.11.1.3.1 states that the modules 
must only be clear of the roof edge by 6’, unless either axis of the building 
is less than 250’ (which is the case at this site), in which case only 4’ of 
clear space is needed on commercial rooftops.

 

 

Will let you all know if it holds up.

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

Lead Systems Designer for:

Dovetail 2013 cmyk 300dpi.jpg

 <http://www.dovetailsolar.com> www.dovetailsolar.com

Ph: 740-274-0139

 

We’ve completed nearly 400 renewable energy projects!  Check out a few in our 
photo gallery:   
<http://www.dovetailsolar.com/Our-Work.aspx?path=commercial+-+solar+electric> 
http://www.dovetailsolar.com/Our-Work.aspx?path=commercial+-+solar+electric

This email message and attachments are intended only for the addressee.  It may 
contain information which is legally privileged, confidential and exempt from 
disclosure.  If you are not the intended recipient of this message, you may not 
disclose, print, copy or disseminate this message and/or the information 
contained in the message.  If you have received this message in error, please 
reply and notify the sender (only) and delete this message along with any 
attachments.  Unauthorized interception of this email is a violation of 
criminal laws and laws covering electronic communications privacy matters. 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Steven Lawrence
Sent: Friday, August 14, 2015 11:36 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Serviceable equipment on a roof

 

Hi Dan,

I don't know which state you're in, but the state of NJ put out a notice 
stating that solar panels do not require servicing.  This came from the top 
electrical inspector back in 2010.  The link can be found at 

http://www.state.nj.us/dca/divisions/codes/publications/pdf_ccc/ccc_spring2010.pdf

It's located on page 11.  Hopefully this might sway your inspector.

Good luck!

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6086 / Virus Database: 4392/10434 - Release Date: 08/14/15

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to