Jay,
the 71V I measured was the array VOC. 
Accessing the wiring for individual strings is fairly difficult as the 
combiners are high up in a hot attic. I didn't have a lot of time on site the 
day I observed this problem, so didn't gather as much information as I could 
have otherwise. 

A re-wire for more voltage looks like the solution.  With 8 modules in series, 
allowing for a wintertime extreme minimum temp of -30C is really going to drive 
the VOC up there. That looks like Classic 250 territory for a long-term solution
 
-Luke


As   
On May 31, 2015, at 1:23 PM, jay peltz <jay.pe...@gmail.com> wrote:

HI Luke,

To add here.  I'm unclear if you have measured each string or the whole array 
at 71v.  
I would check each string for voc/isc.  

And then if they are consistent, I agree that putting 2 strings in series with 
a new controller might help out.  
You can try it with the MX-60 as you are at only 142v. If it works better then 
a new higher voltage CC would be required for winter higher voc.

Let us know what you find out.

jay
Luke Christy

NABCEP Certified PV Installation Professionalâ„¢: Certification #031409-25 
NABCEP Certified Solar Heating Installerâ„¢: Certification #ST032611-03       
CoSEIA Certified PV Installer 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
sgsrenewab...@gmail.com
719.588.3044
www.sgsrenewables.com

   







_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to