I have a Xantrex C-40 that won't keep its settings. It is important that it does because it is for a maintainer array (80 W) on an AGM battery bank, on an AC coupled backup system. Not only could high voltage damage the batteries, but when the voltage goes over 30 Volts, the AUX relay opens and the grid tie inverter is isolated from the grid.

After numerous sessions of reprogramming, Xantrex tech support sent me a new unit. The problem persisted as before. A new temperature sensor helped, but the settings still drift. It seems that rebooting the charge controller helps for a day or so, but then it drifts again.

The potentiometer settings are way below the calculated setting for 29.4 V, but it still peaks in the high 30s. I check the temperature compensated voltages on the Outback Mate, and the temp compensated voltage runs high.

In a related side issue, the AUX relay of the FX inverters is not based on temperature compensated voltage, which makes setting AC coupling charge set points more problematic.

Has anyone experienced a C-40 CC that drifts in its settings. What would be a good (inexpensive) charge controller to accurately control 80 W of PV?

Thanks,

Drake

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to